Factory Talk View Studio ME (8.00) ERROR I CAN'T FIGURE OUT

JohnnyQuanex

Lifetime Supporting Member
Join Date
Nov 2015
Location
Cambridge, Ohio
Posts
120
Folks,

I've not had this problem before and it is likely something stupid that I did to cause this...

Below is the error message I get when I try to create a runtime application (.MER) for my PV Plus 7 Standard (Using firmware 7)


_______________________________________________________________

*** Start RSLinx Enterprise Conversion Messages ***

ERROR: Unsupported driver detected. Driver name = "RSLogix 5000 Emulator". Description:
Only the Ethernet driver is supported by PanelView Plus 7 Standard Machine Edition applications. Only the Ethernet,
Serial DF1 and Serial DH485 drivers are supported by Compact Machine Edition applications.

*** End RSLinx Enterprise Conversion Messages ***

Validation completed with errors. The runtime application has NOT been created.

_______________________________________________________________

I haven't had this happen before; I was trying to setup the emulator awhile back so I could run in design time from my desk, but I don't know what to do or how solve this problem...

Hope you can help...

Thanks so much in advance...

John Whited
 
I'm not sure you can create a MER with the link being the emulator.
You can try the aplication with the emulator, just using the test function...
 
Yes, RSLinx Enterprise is the core driver that gets embedded/downloaded into your target HMI.

In that respect, it should be no surprise that it doesn't support the Logix5000 Emulator.

As jmsmoreira suggests, the programming software should support the emulator in test mode.
 
Open RSLinx
Then: Configure Drivers

If there is a driver 'RSLogix 5000 Emulator' click on it & click on the Delete button in the lower right

If the driver does not exist then something else has it, maybe check RSL5000 itself.
 

Similar Topics

Hi all, Attached below is an example of what is happening to our existing SCADA. It seems after patching some Rockwell Software that I thought...
Replies
9
Views
320
The client has an application that when communication between the PLC and the Factory Talk VIEW supervisory fails, the object in the supervisory...
Replies
5
Views
287
Hello all, I am looking for a way to have a user get logged out after an X amount of time because to default so that user privilages are no...
Replies
4
Views
589
Hello everybody. I was wondering if there is a way in FTVIEW Studio to close ) view after x min without interaction . My issue is the following...
Replies
2
Views
364
Is there a way to choose the base font in ME. Text in the Arial Unicode MS which is the default font on my FTVS doesnt show up properly on a...
Replies
1
Views
678
Back
Top Bottom