Powerflex 525 drive.

Prayder

Lifetime Supporting Member
Join Date
Jun 2014
Location
Arkansas
Posts
254
Question....We have a new Powerflex 525 drive that we have set some parameters in but every time it is powered down and brought back up the parameters have been reset back to the default. We have other powerflex 525 drives that don't do this so I was wondering does anyone know of a setting or something I might be missing? I don't remember one..
 
If it is being controlled by a controllogix processor, make sure that "ADC" is not enabled in the drive configuration of the CLX program. "ADC" (automatic device configuration) would do exactly as you are describing.
 
If it is being controlled by a controllogix processor, make sure that "ADC" is not enabled in the drive configuration of the CLX program. "ADC" (automatic device configuration) would do exactly as you are describing.

That seems to have worked... Thank you!!!
 

Similar Topics

Hi all, I have a powerflex 525 where there is no voltage coming out to the motor. The drive was reset to factory defaults with stop and saftey...
Replies
13
Views
2,738
I had to replace 3 PowerFlex 40 multi-drives that each had 3 PF4M daisy chained off the DSI port. The PF40s had comm-e cards installed for...
Replies
9
Views
2,408
Hi I have a powerflex 525 that is connected on ethernet to a compactlogix and is on ADC , I have just changed a setting on the drive and if I...
Replies
4
Views
1,808
I have a machine with a CompactLogix ver20 and PowerFlex 40 multi drive node. That PF40 has a Comm-E ethernet adapter and has four PowerFlex-4Ms...
Replies
0
Views
1,877
So we replaced a PowerFlex 525 drive with the exact same model. I was told that once it is in and given the old IP address, you can upload the old...
Replies
24
Views
14,218
Back
Top Bottom