Error 701-8004250a

VickyPumero

Member
Join Date
Aug 2015
Location
Miranda
Posts
6
Helloooooo.

Help meee

I have an Ethernet network ip. In the network is a 1969-L32E controller, within the architecture of the controller are two devicenet cards, twenty PF525 inverters, one panel plus 1250. Additionally I have 2 Producer -Consumidor to 2 other controllers.
Having a total of twenty-six CIP connections.
If I disconnect the 525 drives from the network I can connect online normally.
I make the edits and then start to set the inverters to the network again. When you connect the eighth inverter, it automatically disconnects the laptop or a PF525 drive randomly.

Already increase the RPI to 300ms.

Delete all the devicenet network and all the devices that belonged to it, only the devicenet cards were left in the architecture of the controller.
 

Similar Topics

Problem Faced: • We are unable to connect with CPU via Rslogix 5000 • Whenever we try connecting we receive an error “Error 701-8004250A.Failed to...
Replies
5
Views
19,636
Hi Everyone. Not posted on here for a long time, but I am hoping someone can help me. I am doing a differential pressure calculation in a L27ERM...
Replies
9
Views
67
Hello Everyone, I have a issue with communication between two different PLCs. So here is the facts, The Master PLC is Guard Logix 5069 with IP...
Replies
4
Views
81
Hi Siemens guys! I am experiencing SF fault on our S7-300 (6ES7 315-2AH14-0AB0) CPU from time to time. I've checked the diagnostic buffer and...
Replies
13
Views
172
Hello..I am new to Plc.I have Mitsubishi Melsec Fx3Ga-40MR PLC controlling a machine for packing powder.Currently the Plc has issue which power...
Replies
3
Views
139
Back
Top Bottom