I am trying to use the transformer with dual secondary voltages which are 120VAC and 220VAC out of the transformer. I am not 100% sure if I am connecting ground wire on the right spot.
Please see the attached picture.
I connected the ground at neutral.
Can somebody tell me if that is right?
And what if I connect the ground to X4 instead of Neutral? What can happen?

T.jpg
 
For your conventional 240/120 center tapped system, your neutral is your "grounded conductor". And that is where you bond it at the source (Your transformer in this case).

If you were to ground at X4, the transformer itself would not care. But you would have 120VAC potential between your Ground and Neutral, and any devices you connect to that would possibly have some major issues. Not to mention the safety hazards with personnel servicing it in the future and potentials not being what they should.
 

Similar Topics

I just created a hydrostatic pressure testing unit with a PLC and many other devices. The PLC, relays, power supplies and hmi are all located in a...
Replies
12
Views
1,849
Context: Mitsubishi Q series Hi, today I configured an analogue input into the PLC. Then I injected 4-20mA at the terminal block. The digital...
Replies
47
Views
11,504
Dear All, I'm a beginner in the PLC world, please show me the way to learn PLC from the very basic. Really appreciate for your help Warm...
Replies
8
Views
2,240
We've got some job openings around here for full time PLC/HMI dudes. Where's the proper place to post resume requests? Monster and all the...
Replies
10
Views
2,484
I received an email from a student with the following code attached. This is supposed to control a floodgate system, and supposed to be written...
Replies
23
Views
778
Back
Top Bottom