khalid_mahmood
Member
We are using Powerflex 700 VFD to drive the starting motor of gas turbine. Reference speed signal to VFD comes from AB control logic PLC. When we give a start command to the turbine On crank mode PLC give a ref. speed of 36 Hz to VFD but VFD rotates the motor upto 12 Hz in 80 sec after that turbine stopped at fail to crank alarm. During running the out put voltage of VFD fluctuate. After reset of alarm we immediately give the second start command to turbine. This time the motor rotated upto 20 Hz in 80 sec after 80 sec turbine stopped on fail to crank alarm. During the second attempt the out put voltage and frequency increase smoothly upto 15 Hz with out any fluctuation above 15 Hz out put V/f again fluctuate. The parameter of VFD are same as when it was running normally. Kindly guide where is problem.