Hello all, I am stumped. Here it goes;
I have a 1769 L33ER (PLCA) connected to a Stratix switch A with the latest firmware 15.2(4) non ******. The switch connects to a panelview plus and 4 1794-AENTs. This switch is feed from another switch(B) in the same control panel. Switch B is a Stratix 5700 with the same firmware. This switch talks to a Compactlogix PLC B as well. PLC A is wire framing but for the wire framing periods I can ping the PLC processor from the Server and none of the local Ethernet I/O drops out in addition the local panelview plus remains polling data. But the clients wire frame.
Things I have tried. Upgraded all switches to Stratix 5700.
Rebooted both redundant Virtual Server Computers. These contain our data servers and HMI server etc....
I direct reference a tag on this screen without using HMI tags and it wire framed.
I used Factory Talk Live Data test client and the data drops.
I exported the tag database and re-imported. No help.
I re created the shortcuts in Rslinx Enterprise.
I have the ports set to autonegotiate and I have been told I should try hard setting them to 100 Full.
I have played with the overhead time slice.
From the switch connected to the processor having issues I can always ping the server even when wire framing.
Previously we had unmanaged N-tron switches installed so they must have been set to autonegotiate.
I wonder if the processor could be bad. Can anyone tell me what messaging Rockwell uses for panelviews and Aent modules and if that is different for the messages to Factorytalk?
Could only part of the PLC internal Nic card be failling?
Any else I can try. Rockwell recommended Smart ports on the Stratix Switches but this is the only processor in the plant that is having this issue.
I have a 1769 L33ER (PLCA) connected to a Stratix switch A with the latest firmware 15.2(4) non ******. The switch connects to a panelview plus and 4 1794-AENTs. This switch is feed from another switch(B) in the same control panel. Switch B is a Stratix 5700 with the same firmware. This switch talks to a Compactlogix PLC B as well. PLC A is wire framing but for the wire framing periods I can ping the PLC processor from the Server and none of the local Ethernet I/O drops out in addition the local panelview plus remains polling data. But the clients wire frame.
Things I have tried. Upgraded all switches to Stratix 5700.
Rebooted both redundant Virtual Server Computers. These contain our data servers and HMI server etc....
I direct reference a tag on this screen without using HMI tags and it wire framed.
I used Factory Talk Live Data test client and the data drops.
I exported the tag database and re-imported. No help.
I re created the shortcuts in Rslinx Enterprise.
I have the ports set to autonegotiate and I have been told I should try hard setting them to 100 Full.
I have played with the overhead time slice.
From the switch connected to the processor having issues I can always ping the server even when wire framing.
Previously we had unmanaged N-tron switches installed so they must have been set to autonegotiate.
I wonder if the processor could be bad. Can anyone tell me what messaging Rockwell uses for panelviews and Aent modules and if that is different for the messages to Factorytalk?
Could only part of the PLC internal Nic card be failling?
Any else I can try. Rockwell recommended Smart ports on the Stratix Switches but this is the only processor in the plant that is having this issue.