Trying to use a alarm banner but it is asking
for an event. So what is it asking for
Do I need to create an event item will all the alarm
tags in it
 
It is waiting for an ALMD or ALMA instruction to be triggered in the controller.

You will also need to enable FT Alarms & Events in both the RSLinx Enterprise settings as well as the controller shortcut.
 
Trying to use a alarm banner but it is asking
for an event.

Do you mean it's sitting there saying "waiting for alarm events"? That's just the message that is shown when there are no alarms or events to show, it's basically saying "everything is good, I'm just going to sit here and wait until I have something to show you".

Is it saying this when it should be displaying alarms/events, or were you just wondering why the message was there?
 
I want to use the banner to display standard HIM alarm tags not sql alarm tags,I think it is asking for an SQL alarm server connection
 

Similar Topics

Hi guys, Got a little bit of a strange one... I'm using FTView ME v13 with a Panelview Plus 7 B (the new one win 10 based). Alarms were...
Replies
4
Views
991
I've been messing around with trying to find a way to clear all PlantPAx AOI latched alarms via the Alarm Banner or Summary objects. So far, I can...
Replies
2
Views
1,734
Hello, I have an application with a CLX L8 running under firmware V31 and an instance of FTView SE version 11. I configured a logix based...
Replies
4
Views
2,049
Hi. I'm trying to get the number of alarms from an alarm and event banner located on a display called "alarmepag1" and write to a HMI tag...
Replies
1
Views
1,883
Hello all, I am doing this work remotely, so I am not completely able to explain what is happening, but I am getting reports from operators...
Replies
11
Views
2,543
Back
Top Bottom