In search of single phase;phase monitor for 240v with modbus comms. Just need to monitor voltage and amps. Or I like to monitor voltage with a AB micro800 or 1100, any ideas? I can use Analog CT for amps.
 
In search of single phase;phase monitor for 240v with modbus comms. Just need to monitor voltage and amps.

Wago has input modules for power monitoring, can do voltage, amps, active, reactive, apparent power, cosinus phi etc. Used in conjunction with transformers or Rogowski coils.

Wago modules 750-493, 750-494 or 750-495 depending on how you get your input (transformers, Rogowski coils). If used through Modbus/TCP then you would additionally need a 750-352 (fieldbus coupler for remote I/O over modbus/TCP) and an end module 750-600. The modules are designed for three phase and when used with remote I/O costs add up so this may not be cost effective for you, especially if you only measure a single phase.
 

Similar Topics

I have an existing power meter with 200:1 current clamps with 1.8 ohm burden resistors. I am replacing the meter with a Powermonitor 1000. Reading...
Replies
2
Views
1,756
Hi guys, may be an obvious answer to this question but I'm a total noob to AB powermonitors. Our IT department wants us to change IP addresses...
Replies
3
Views
1,750
We currently have an RSEnergyMetrix server in place that allows us to pull data from all of our PowerMonitor 3000s. We would like to pull this...
Replies
0
Views
1,655
Hi, I have huge problem with sending data from PM500 to ML1100. I'm using rs485 connection with ml1100 as modbus master. When i try to read from...
Replies
2
Views
2,129
I am using a Allen Bradley Powermonitor 3000 on a DNET network and I require it to be Node 5, however when viewing it at the dispaly the address...
Replies
6
Views
2,567
Back
Top Bottom