Looking closer at what you have posted, and correct me if I am wrong, you are using the AOI to populate the PREsets of your sequence timers. The StepTimes are defined in the sequence UDT in seconds, so the MUL instructions are converting these to mS values for use by the sequence timers.
There is no need for the Timers to go into the AOI at all. If you change your MUL instructions destinations to DINT output parameters, flag as "required", then you can achieve the MOVs to the Timer presets in the AOI instruction "box", just specify each timer preset as the out parameter destination for each of the new DINT parameters.
Now, I'm surmising that your sequence logic has a timer for each step... does it need to have any more than one timer ?, and does it need to have a preset ?. Your sequence of (up to) 32 steps would require 32 timers... what if the sequence had 320, or 3,200 steps ? Using a separate timer for each step starts to look like there ought to be a better way.
The sequence control logic I use has only one "StepTimer", with a preset of 2,147,483,647 (max). My actual sequence only needs to test if the StepTimer has reached (or exceeded) the required StepTime, to transition to the next step, and the timer is reset on each step transition. I have an AOI called from my sequence control logic AOI that calculates and populates a UDT that expresses the StepTime as milliseconds, seconds, minutes, and hours (REAL values), so my sequence can do GEQ any one of those...
Of course you may not be able to re-do your logic, but bear this in mind for the future. I could quickly piece together an example of the methods described, but can only go up to V24.