Flow control of waste water stream

SLaubach

Member
Join Date
Apr 2002
Location
PA
Posts
152
Hi all-

Looking for a stand alone valve/controller to regulate wastewater flow to 100gpm. would like to make it a self contained as possible without the use of analog i/o in a plc.

what i have is a treatment plant running without any plc's (all hardwire) they are now required to dischage only 100 gpm to the local sanitary authority. I have found a nice magnetic flowmeter (sparling) that will output 4-20 or 0-10. my problem is i cant locate a valve capable of scaling the signal internally without the use of a plc.

any help or advice is greatly appreciated!
 
A simple mechanical solution would be to calculate flow based on the area of the opening and static pressure on the supply side.

I cant thik of the equation right now but GPM is a factor of pressure, viscosity, amd the flow opening area.

Presumeably you have an overflow basin of some type. So lets say you provide a discharge tank with a fixed opening/valve at the bottom. A overflow/spillway at or near the top of discharge tank would in effect regulate the pressure behind the opening at the bottom of the discharge tank. Any overflow would be returned to the overflow basin by gravity. Your entire control system would be a simple level switch to turn off the pump filling the discharge tank when it starts to overflow. No PLC, flow meters, etc.. required. In short a small water tower.
 
There's a category of commercial instruments known as single loop controllers that are designed to control a modulating valve.

The input signal is typically 4-20mA from a magnetic flow meter, the control algorithm is known as proportional PID control, and the output is 4-20mA.

The 1/4 DIN single loop controllers are designed for panel mounting, are run from AC power, have a couple display lines to show the process variable (actual flow) and the setpoint (100gpm).

Most if not all single loop controllers have some form of auto tuning nowadays, so that one doesn't have to fool around with tuning the loop.

We use the Honeywell UDC line, other brands are Yokogawa or Siemens.

Dan
 

Similar Topics

Hello All Could we get some expertise on flow control ? -Using a PID loop in Productivity 2000 with an analog output, How can we convert...
Replies
19
Views
1,580
Hello: I am experiencing the following error: [ERROR] C0297: Stack overflow detected in DecodeOID. Maximal Stack Size: 64512. Calculated...
Replies
8
Views
1,217
Hi all, i'm after some help on a flow control valve control strategy. There are 8 parallel vessels that require evenly distributed flow. Each...
Replies
32
Views
6,970
Hello all, I am new to pid loops and control. I was wondering how to control a system with two process variables. This is a water system with a...
Replies
7
Views
2,008
Hey everyone, I was on a customer's site on friday where they have a large bioreactor that they bought secondhand from a previous user. System is...
Replies
22
Views
4,469
Back
Top Bottom