Danfoss VLT Micro FC51

chud

Member
Join Date
Oct 2007
Location
KALAHARI
Posts
1,122
Hi Guys
Took over a job where the customer has VLTmicro fc51 drives. Im installing a plc to control them so I would need a digital input from them telling me if they are tripped. I have never used these drives before
There is no relay outputs on these drives. The only thing I found in the manual is that you can switch the analog output to a digital output via paramater 6-90 and 6-92. I have done this but still dont get the contact to react. Just get a permanent 18Vdc out.
Is there any other settings you guys know of?

Thanks for any advice
 
Your PLC input likely presents insufficient load for that solid state (converted) output, your PLC input is reading the leakage current regardless of the state. You may need to experiment with burden resistors or at the very worst, use the VFD output to drive an interposing relay and the relay to give you the input to the PLC.
 
most VFD have relay output for VFD status

He makes a good point. I took it at your word that you said this drive has no output other than the convertible one, but I just looked at the manual and there is indeed a relay output. 01, 02 and 03 terminals are a Form C relay. 03 is common, 01 is NO and 02 is NC. The functionality is programmed in 5-40.

RTFM...
 

Similar Topics

Hello everyone, I am an engineering student who took on a project to design and build a control system for an industrial coffee roaster as my...
Replies
16
Views
4,422
Hello all. I am hoping someone here has installed a Danfoss VLT Midi FC 280 and connected an encoder to it. I am just trying to make sure I select...
Replies
0
Views
445
Having a small problem with a new danfoss micro VLT FC51 drive I was hoping someone on here could help with. my setup: my motor speed is...
Replies
4
Views
1,397
Hi all, Got a Danfoss FC102 VLT drive which reverts to Off mode whenever I cycle power to it. I'm controlling it over ethernet from a Control...
Replies
2
Views
1,808
Hi all, I am having a problem with 3 VLT 2800 drivers. All are showing on occasion error 16. I know that this points to short circuit on the...
Replies
0
Views
2,275
Back
Top Bottom