PLC Schneider Electric Zelio Logic SR3, lost ethernet connection after electrical ene

rlaviles

Member
Join Date
Mar 2017
Location
Santiago
Posts
3
Hi.
I am, in fact, not an specialist in PLC's but, in my work we remotely access a gear 500 kilometers away and we have observed, after some electrical energy glitches, power outages, one of the components of our system, a Schneider Electric PLC Zelio Logic SR3, lost its connection through the ethernet, so far being the only solution to ask someone else around to unplug and then replug the ethernet connector.
The ethernet connection is provided by a Cisco Catalyst 3500 and, as far as other components easily/promptly recover after a power outage, it seems to be our only problem is the PLC.
I will appreciate if someone -please- can give me a suggestion. Whoever programmed the PLC is not here, that is why I am searching for possible answers.
Thank you very much in advance.
 
This is probably due to the sequence that things are starting up. Can you replicate the situation manually?
If so, then you may need to delay the start of the PLC until other components are powered up.
Another option is to try and keep the PLC active longer by the use of an uninterrupted power supply. (UPS)

Regards,
 
Good Morning gclshortt.
Thanks for your reply. At less now I cannot replicate the failure, because I am far away of that location. We are considering the use of batteries as a way to back-up the PLC. However, the other workaround looks more interesting: "delay the start of the PLC until other components are powered up."

Please, I will appreciate a suggestion, hint, clues, tips.... on how to do that. As I say this is a Schneider Electric PLC Zelio Logic SR3 B261BD. I can see one Zeliosoft2 Diagram, which I guess is the one but, I do not have a clue on what to do ;)

Thanks in advance!

Roberto
 

Similar Topics

I am using a M221 PLC (TM221CE24R) which provides me 1 Rs485 port, which I am already using to communicate with a sensor (Rs485/Modbus). My...
Replies
1
Views
732
Hello, I am trying to detect when the PLC changes from STOP to START mode. This can be considered an edge case scenario, but I would to analyze...
Replies
4
Views
1,530
I need some help with a Schneider Electric TM221CE40R controller. A customer wants me to add a few level switches and do some basic programming...
Replies
3
Views
1,611
Hi, Sir anybody know the link for the programming software Schneider electric LMC058. i NEED TO UPLOAD THE PROGRAM FROM LMC058 Motion...
Replies
1
Views
3,255
Dear sir, I've Schneider electric Quantum series hotstandby plc 140cpu67160 and unitypro XL 2.3V and OS loader 2.31V.I've problem that when power...
Replies
1
Views
6,847
Back
Top Bottom