Sorry to chime in late on this topic, Mike. The consensus seems to be to use an HMI, which is what I would recommend also. The onboard pots can be handy, but as Keith mentioned, adjusting them without seeing the value would be confusing for the operators.
I have used them in the past on occasion, but in conjunction with an HMI. Back then, I was using the Optimate panels, and providing timer adjustments was a chore. What I did was simply let the user display the pot's value on the screen so they could SEE the setting.
I have also used them as discrete switches to turn options on and off. With the min/max values set as 0 and 1, fully CCW = OFF, and fully CW = ON. Eliminated wasting an input for rarely changed selections...
elevmike said:
The Pots/timer adjustments are to be used just for inital setup, and VERY infrequently thereafter. I need a way to adjust the timers that would be very intuitive to a non-plc type tech.
Here's my low-cost, operator-friendly solution...
Optimate OP-420 display and cable to port 1 - $145 (that's the low-cost part). I would use an Optimate over an EZ-Text because they get their 5V from port 1, so it's a cinch to connect/disconnect while the machine's running. No separate power supply connections. They can just plug it in whan they need to, freeing up port 1. Also much more comfortable for handheld use. No A-D 'bat wings' getting in the way...
Create a simple menu of timers that the operator can navigate with the function keys (F1 - Previous, F2- Next). This will display the names of the timers and their current setting. If an operator wants to make a change, they scroll to the respective screen and press F3 to request the change.
Now the display shows the current setting on the top line (for reference), and the value from the pot on the lower screen. The operator adjusts the pot to get his new setting and presses F4 to 'enter' the new value. This writes the pot's current value to the timer preset.
If the operator decides not to 'enter' the new value, they can press F3 again to abort the change, and return to the timer menu. Always give them an 'oops' choice!... :nodi:
This would require minimal programming in the PLC.
beerchug
-Eric