Allen Bradley Guardmaster safety relay Low Voltage on S12 and S22

Join Date
Aug 2016
Location
Virginia
Posts
343
Good Evening ,

I have a Guardmaster Safety Relay I have 14 vdc on S12 (Safety Input for IN1 Channel 1) and on S22 (Safety Input for IN1 Channel 2) I have 18 vdc. On S32 ( Safety Input for IN2 Channel 1 ) I have 23.51 vdc . On S42 ( Safety Input for IN2 Channel 2) I have 23.51 vdc. I am having a difficult time resetting this safety relay. Do these safety relays have a internal power supply ? Do these voltages concern you any ? I believe it is a 440R-D22R2.

Thanks so much in advance ,
 
The lower apparent voltages are because you're measuring the pulse-tested sources: S11 and S21 send out 24V pulses at different patterns and rates so they can be differentiated. An ordinary digital meter will measure these as 14V and 18V (respectively) because that's what they average out to.

https://rockwellautomation.custhelp.com/app/answers/detail/a_id/1040292


You're measuring those voltages on S12 and S22, which makes sense because those are the signals from the pulsed sources, having traveled through the e-stop relay contact or whatever you're using as a sensor. S12 and S22 are Channel 1 and Channel 2 of Safety Input 1.

But the fact that you are seeing a more nominal 24 V on the Channel 1 and Channel 2 inputs for Safety Input 2 suggests that those circuits aren't sourced from the pulsed S11 and S21 channels or from a OSSD style safety pulsed output.

What's the difference in the devices that are connected to Input 1 and Input 2 ?

Was this relay working correctly at some point ?
 

Similar Topics

Team, I have had some issues with my MCR dropping. This is an issue that has been in 2 of my lines prior to me coming to this facility. The...
Replies
4
Views
2,031
Good Afternoon , We have a number of these Allen Bradley GuardMaster Safety Relays in the plant. We had a problem with a safety circuit...
Replies
3
Views
1,948
Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
10
Views
207
Dear community, I am trying to find a tool for Allen-Bradley PLCs similar to SiVArch for Siemens PLCs to automatically generate faceplates and...
Replies
0
Views
76
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
13
Views
413
Back
Top Bottom