I have a Panelview 550 (2711-K5A2) and a Micrologix 1200 (1762-L24BWA). I want to connect the two together point-to-point. My question is... What is the easiest fastest and cheapest means to do this? Can it be done with just a cable or do I need a link coupler(s)?

Thanks in advance for all your help!

Standard Machine
 
The K5A2 is DH485.
You will need to use a link coupler (AIC or AIC+)

Remember to set the ML to DH485 as well.

PV - AS03 cable -- AIC+ -- PM02 cable -- MicroLogix

You may need to provide external 24vdc to the PV
2711NP1 I believe
 
THANKS!

That's what I needed to know. I was aware of the need to change to DH-485 on the ML1200. The only issue was how to connect the two together. Thanks Again.
 
I have an issue with the same panel view and micrologix.

I have the PV and the ML connected with DH485 with the coupler but i dont have communication.

i verify the nodes and everything its alright do you have any idea?



I already had connected but i have to change the PLC because got failed but its the same model of PLC but when i try to connect with the PV i dont have conecction.
 
Tell us the complete catalog number of this "coupler" and also tell us the cables you are using to connect everything together.

Also if you can post the programs of your PLC and the PV. Zip them first.
 

Similar Topics

Hey all! Long time reader, first time poster! I have an EA9-T7CL and an MicroLogix 1200 connected via DF1. I'm all good and got everything mostly...
Replies
3
Views
648
Hi every master,Recently i met a fault about 1762-L40BWA 1,When i get the PLC, The Fault light is lighting, I am not remember the fault message,I...
Replies
0
Views
718
Hello everybody and master,I met a problem about ML1200.It is described as below: 1,When i got this PLC,The FAULT light is lighting, My computer...
Replies
4
Views
1,104
I had planned to use PTO instructions to control a servo motor, single axis only. We have a ML1200 BWA model. According to the ML1200 manual...
Replies
7
Views
3,478
I am using Modbus to read 36 registers from a ML1200. 2 of those registers are suppose to be L11 data and 2 of the registers are F8 data. Long...
Replies
3
Views
1,379
Back
Top Bottom