I'm on site at a customer's facility. We're using solid-state relays to control heaters in two halves of a manifold and a heated hose supplying the manifold. My boss said prior to start-up, that on-off control would be fine but the customer isn't happy with the overshoot (about 10-15°F).
I did some googling last night and I've put in a PID instruction in a periodic task, set at 0.1ms period. I've tested this by toggling a bit every scan and counting off-on transitions and I'm getting 5 counts per second. So the task appears to be running. The PID instruction update rate is also set at 0.1s. I'm using the output to give me time proportioning control of the heater SSRs (or will be if I get it working).
The problem I have at the moment is that the output of the PID loop is not moving from 100%. When I change the control action from SP-PV to PV-SP, the output ramps down to 0% but then it stays there too.
I've not actually got the PID instruction controlling heaters yet, I'd like to have some confidence that it's going to work first.
I'm using a 1769-L16ER-BB1B. With 1734-IR2 RTD modules connected to 120ohm Nickel 672 RTDs. The modules are configured as
Sensor: 120ohm Ni 672, Temperature units: Fahrenheit, High engineering: 5000, Low Engineering: 1000, Digital filter: 0.
I'm not entirely sure what the engineering units mean. I'm fairly certain that they're the default values. The user manual for the module says that the low scaling endpoint is 32°F and the high is 482°F. We've seen temperatures in the range 75°F to 250°F and the temperatures seem accurate.
I'm hoping someone could take a look at the attached screenshots and offer some advice as to why it's not working. Thanks in advance.
I did some googling last night and I've put in a PID instruction in a periodic task, set at 0.1ms period. I've tested this by toggling a bit every scan and counting off-on transitions and I'm getting 5 counts per second. So the task appears to be running. The PID instruction update rate is also set at 0.1s. I'm using the output to give me time proportioning control of the heater SSRs (or will be if I get it working).
The problem I have at the moment is that the output of the PID loop is not moving from 100%. When I change the control action from SP-PV to PV-SP, the output ramps down to 0% but then it stays there too.
I've not actually got the PID instruction controlling heaters yet, I'd like to have some confidence that it's going to work first.
I'm using a 1769-L16ER-BB1B. With 1734-IR2 RTD modules connected to 120ohm Nickel 672 RTDs. The modules are configured as
Sensor: 120ohm Ni 672, Temperature units: Fahrenheit, High engineering: 5000, Low Engineering: 1000, Digital filter: 0.
I'm not entirely sure what the engineering units mean. I'm fairly certain that they're the default values. The user manual for the module says that the low scaling endpoint is 32°F and the high is 482°F. We've seen temperatures in the range 75°F to 250°F and the temperatures seem accurate.
I'm hoping someone could take a look at the attached screenshots and offer some advice as to why it's not working. Thanks in advance.