If it were me, I'd be putting it on a 4A C/B. The main thing you're protecting is the wiring, not the appliance.
This is the point. You are not protecting the downstream device, but the supply wiring to it.
Fuses are to prevent fires. Even ultra fast fusing/breakers do virtually nothing to prevent damage to the connected device, even if on replacing it the device begins to 'work' again... more times than not, it is at least slightly damaged, and is only going to get worse with time.
But since you are curious, the specs on the power supply tell you that under perfect circumstances, it can put out 6A at 24VDC, which means 144W, not 120W, so 144W at 120V at a .7 power factor = 1.71A, not 1A (you also forgot Power Factor when converting DC Watts to AC Watts). On top of that, inexpensive Switch Mode Power Supplies like this are typically around 60-65% efficient line to load (as this one appears to be). The very best are maybe 85% efficient.
In a DC circuit: A x V = VA, but also WThanks everyone for the answers! Sizing the wiring is the easy part. It's calculating the fuse size that's confusing.
Ok, Explain the calculation like I'm 5...How did you get "144W at 120V at a .7 power factor = 1.71A, not 1A (you also forgot Power Factor when converting DC Watts to AC Watts)"?
So what did we just calculate with 1.71A? How does that relate to the 2.6A on the label?