Hi AB experts,

I need your help to solve an issue in SLC 05/03 cpu. Fault is blinking continuously and it's not in run mode. moreover all input cards having the supplies but not output cards.

could you please tell me the way to out...
Thanks in advance:)
 
Output cards will not function unless the processor is in run mode executing a program. So first thing is to discover what the fault condition is. That can be done by connecting with rslogix 500 software.
 
Hi Jstolaruk, First of all thanks for your reply.

I am unable to connect to PLC through RSlogix due to communication error.

I have 1747-UIC adapter to establish communication between PC and PLC. But unfortunately, I couldn't succeeded in many attempts.

Please tell me the procedure to connect ..Thanks in advance.
 