Hi again guys,

I have this system where I need to monitor/control 24 incubators.

Most have reasonnable Setpoints and margins of error, thing like 40°C± 2.0°C

The problem I have is that some of them have a Setpoint of 4°C while the margin of error (read diff. Alarms)is ±0.2°

This 0.2°C really bugs me.

I can have RTDs or even TCs with 0.1C resolution but the input modules for PLC add more error than I can live with.

My typical RTD would have a resolution of 0.089°C but the darn input cards don't match this.

Normaly its not a problem when we read something in the hundreds of degrees but at 2°C its BAD!

Do you guys know of converter modules (Ex: ModbusTCP) that can accept a 100 Ohm RTD (3 Wires) that are not crazyly expansive?

Know I'm at $350 a point for a 0.01 resolution and $200 for 1°C ...

What I need is a cheap way to read temperatur from -10 to +50 C ±0.01°C and bring it into a PC with a SCADA.

24 times.

Any suggestion is welcomed.
 
I'm not sure of the resolution, but DGH Corp and Advantech have analog and temperture modules that communicate over a serial link (I thihnk with Modbus RTU). You might check them out.
 
Hi Pierre

A similar question was asked recently and I suggested a look at Red Lion Controls Modular Controller. This controller / Data acquisition system has a resolution of 0.1c and can communicate with a number of PLCs and I beleive with a PC over ethernet. It can have upto 16 modules with 4 or 6 inputs on each module.

Red lion's web site is www.redlion.net

Jim.
 
You may try Omron from the initial search temperature input modules
D2t1-tso4p
or qt1-tso4t or 4p

both of them had an accuracy of 0.1 c or 0.3%
 
I have seen many x-mitters and what could be the most accurate for me is not to go through a PLC but directly into a PC with the x-miter com. ...

Its only that I need 0.01 C precision ...

...and most x-mitter altough they have an ana analog resolution of 15 bits and more ... they have a digital resolution of 8 bits. ... firmware vs packet size stuff I figure!!!

Still searching to get 0.01C not % into my PC the cheap way :)

I will check out those leads thanks.
 

Similar Topics

We have a small plastic parts oven (SP at 210F). It used to have an old bimetal temperature regulator. We are upgrading it using two temperature...
Replies
7
Views
1,529
Needing some help. I have a machine that was put in storage and has ended up in my lap. It had a 5/02 originally but the card was pulled and I...
Replies
3
Views
1,410
I'm tasked with replacing a process's temperature controllers (which feature PID autotuning) with PLC control. Do any PLCs feature PID autotune or...
Replies
33
Views
10,216
Hello I have DTC 1001 and DTC 2001 delta Temp control connected to together as one unit , and this unit connected to SS2 plc via Rs485 , My...
Replies
0
Views
1,029
We are currently running 3 point temp control of a kiln and recently had a thermocouple failure which caused issues with our heat up cycle. In...
Replies
8
Views
2,328
Back
Top Bottom