Is this a project that has worked in the past, or a new one that you are creating for that old PanelView hardware ?
I noticed that your Communications Setup defines the Node named "ADMIX" as an "Allen-Bradley PLC". I think that means that the PanelView expects PLC-5 style data table addresses instead of the ControlLogix tag names you have for the addresses of those PanelView Tags.
Check that configuration to see what options are available for you to tell the PanelView that the target is a ControlLogix, with a CIP Path to the CPU.
Your addressing also shows one PLC-5 style address (F221:188) but the rest of the addresses as actual ControlLogix tag names.
The PanelView Standard's support for ControlLogix tag names was gradual and imperfect; I would have to get out a bunch of references to tell you what version of PV550 firmware fully supported ControlLogix tags.