Channel 0 RS485 modbus communication

Join Date
Dec 2017
Location
Bangalore
Posts
3
I am trying to setup the master and slave for my ML1400 PLC using 2 core ( Tx-1 & Rx-1) RS 485 modbus communication. I received the data as my ML1400 channel 0 set as Modbus RTU master. I am trying to send my data with the same RS485 communication. How to setup the message instruction for that.
 
RS-485 always requires 3 conductors; Data +, Data - and Data Common.

If your other device doesn't have a dedicated Data Common terminal or pin, connect the Pin 2 "GND" on the MicroLogix 1400 Channel 0 port to the Chassis Ground for that device.

The MicroLogix 1400 RS-485 port is non-isolated and is not recommended for long distance communication.
 