Allen Bradley Powerflex 753 Drive Error

Nandraj

Member
Join Date
Dec 2016
Location
India
Posts
51
Dear All,
I need urgent help for my powerflex drive 753 showing error

port x06 not functioning (conflicts) i tried to find out soluction from allen brad;ey site i did according to the solution but same problem persist my drive is new drive

please need idea on it
 
On a 753, you have 3 ports for plugging in accessory option boards to the left of the main control board. Port 6 is the one farthest to the left. What do you have plugged into that port?
 
Chances are you have a problem with your DeviceNet installation; improper configuration, too far from the power supply, no terminator at the end of the trunk, etc. etc. etc. It might just be a bad D-net card too. Did you try swapping it out?
 