Op17 for S7400-H

huynt

Member
Join Date
Nov 2004
Posts
106
dear sir
now, we want to use S7-400H(CPU 414) with OP17s. I use profibus with OP17s. Do you know method connect wire CPU414 with OP17s for redandancy
 
You have to connect the OP17 from a remote I/o rack to the S7-400. It cannot connect to the profibus network, since it will be on one PLC or the other. Both PLCs merge into a remote rack using a Y coupler or a 6es6-157 with an active back plane. Then you can connect serially or Modbus from the active backplane to the HMI using a CP340 or CP341. I've used the TP170B connected with Modbus communications, with a redundant network and it worked fine.
 
Hi!
I have not connected an OP17 to an S7400H, but I have connected a T270/MP370 etc on profibus.
You will need a 2 repeaters to bring both profibus cables into one cable.

The OP project must not be integrated into Step7 (you can develop it integrated, but must unintegrate before downloading)

In Not Integrated Protool go to controllers ->double click on the PLC and click on parameters ->select profibus and make sure that the baud rate matches, etc each panel should have a unique profibus address Under peer parameters the address, expansion slot, and rack should all be 0(zeros).

Now both panels will be talking to whichever CPU has primary control and they will switch when the CPUs switch.

Hope that helps.
 
Last edited:

Similar Topics

I am receiving the following error message on the Simatic OP17 $545 DB 32b 41 3 not avail. Before the restart that this HMI always does...
Replies
20
Views
6,186
Hi. I am looking at a future project of migrating some OP17's to some newer HMIs. I have briefly looked at this & it doesn't seem as easy as I had...
Replies
2
Views
2,293
Does anyone have the old ProTool software from Siemens? I was wondering if someone could open a project for me or sell me the software. From...
Replies
12
Views
7,923
Does anyone have the old ProTool software from Siemens? I was wondering if someone could open a project for me or sell me the software. From...
Replies
0
Views
2,851
I want to up load progam from old OP 17 to PC and then down load to new OP17.For this I need software,Cable connection lay out and the...
Replies
1
Views
1,688
Back
Top Bottom