This is probably a ElevMike question.

The emergency button/phone or whatever signal from an elevator. How is it monitored? Fire alarm system? Security System? or a separate 3rd party monitoring agency?
We are installing a small 2 floor elevator and were wondering what the requirements are for monitoring this signal from the elvator.

Thanks!
 
Not sure what signal your refering to...However:

1) The elevator phone must be ADA compliant..(whole nother set of rules there). The phone should self dial any in house or out of house connection that will be monatored 24 hours a day by a LIVE PERSON. The phone must play a recorded message, when the other end picks up, stating the location of the elevator. After the message is complete then the emergency operator can talk to the people in the elevator. Ususal response is "Opps..I pushed the wrong button". Once in a while there's actually somebody trapped. The elevator company usually has a monatoring service. We do not charge for this service for customers under contract. But we do charge for sending a tech out to extract the trapped...

2) Smoke detectors.. We're still arguing with the inspectors about this, but the smokes that set off the elevator on fire service must be limited to thoes in the elevator lobbys, hoistway and machine room. The elevator will react to only the 1st detector tripped and ignore all other detectors. The elevator controller is usually provided with a dry contact so that Simplex or whoever can wire it back to the main building alarm panels.

3) Shunt Trip Operation: Very badly written part of the code. Most locals havent adopted this part, but it calls for a heat sensor to be placed by each sprinkler head in the hoistway and machine room. In theroy the heat detector will cut off the power to the elevator before the sprinkler sprays water on the elevator equipment. Problem is then people are trapped in the elevator in the event of fire and usually end up roasted, smothered and wet. The State of Michigan adopted A17.1 -2000 but then recinded this section for obivous reasons.

Hope I've answered your question.. The best bet is to check with the elevator contractor and find out what applies in your area..

Word to the wise on new elevators..watch out for propritary equipment..or you'll be married forever...
 
Thanks Mike,

I wasn't involved in the quote and selection process on the elevator. I was out of the country. I was asked how we monitored the "Emergency" push button that will be located in the elevator. Our A&E firm tells me that unless you have a 24hr person at a security console, it has to be monitored by a 3rd party and requires a dedicated analog phone line, which is right in line with what you said. I can't wait to see the spec's on this thing, I'm sure nobody that really knows anything about elevators or what to research was involved with this decision, as usual.

Thanks again.
 
It's simply a case of... as long as an elevator is liable (not just likely) to be used, someone needs to be at the other end of the emergency phone when a passenger picks it up.

The phone should be connected to another phone where there will be a REAL person saying "Hello?"... not just a recording saying that all operators are busy or business hours are such-n-such. In the case of an industrial environment where the plant is occupied by someone all the time (someone other than the poor sap stuck in the elevator) the phone should also activate some sort of sound device to indicate that someone one on the elevator is trying to contact someone... anyone.

If the potential victim is a watchman, all alone on his rounds, then the phone needs to connect to someone outside that can provide help as required.
 

Similar Topics

Hey guys , I have included a couple attachments here , one of what I was supposed to come up with a program and the program I came up with. Does...
Replies
16
Views
3,108
I've been trying to solve an issue that I've had for several days now and it has now made me give up, which in turn led me to this forum in hope...
Replies
7
Views
2,577
Hi I'm new to plc and I've been looking for solutions in 4 floor elevator. I have been studying this elevator solution for like a week now, and...
Replies
4
Views
2,862
Hello, I'm trying to make a 4-level elevator work in SFC, but I feel kinda lost. Could anybody help me with at least the first 2 level SFC? Thank you
Replies
12
Views
3,911
i am making this elevator program in TIA portal I have written a program but it is not complete yet i created two arrays the first array is...
Replies
9
Views
2,215
Back
Top Bottom