Point to point identification of the IO's conected to the control panels of my PLC is needed since the documentation and tags of the wires are missing. The question is if the only way performing point to point verification and identification of where the IO's wires go is shuting down the system?
 
Most of that would depend on safety issues and the location of the I/O.

The fastest way to get it done would be to have the system down. Deactivate the outputs then check the inputs one by one. Output devices should be disconnected from their load and then activated one at a time thru the plc if possible.

This sounds like a long drawn out procedure but it can be quick and allow the time to mark the wires as needed.
 
Have to agree with Ron, best way is with system down. I've done this a few times, here's a couple of pointers. Have two or more people with 2-way communications, radios, cell phones,something. Check the inputs, then write up some type of timed based toggle logic, disconnect all outputs but one, use the toggle logic to toggle the output, have someone in the field, look for the pulsing device, identify it, the move on to the next one.

Good luck,

Ken
 
I have had to do the same thing recently - with the system online and running. Had a few incidents where when the electricians were tracing wires they pulled the wire out due to loose connections. This led to a quick thermal scan to find loose connections.

Overall, went well and got point to point checks and drawings complete.
 

Similar Topics

Hi, I have some problem with View Point which I'm using to manual control of conveyors. On begin when in network was only PLC and HMI View Point...
Replies
0
Views
73
I have a bunch of tags in Historian/VantagePoint that off by one decimal point. I looked into the HMI displaying the same number, and the HMI is...
Replies
2
Views
115
Good morning, I have a Emerson/GE PLC with Cimplicity SCADA. I need to export data of a specific point/object to a CSV file and load the CSV file...
Replies
7
Views
280
Dear We are working in AB Studio 5000 and the drive is a PowerFlex 755T. For this project I need to control a conveyor to a certain set point...
Replies
2
Views
136
Hello colleagues Anybody knows, what could be the best or a better option to bring with you when you are in service at factory to connect via...
Replies
1
Views
261
Back
Top Bottom