can anyone tell me how long i can make my DF1-cable (the length the 1747-cp3 has is not enough)

and if this should by quite short, how long can the branches be on an AIC-network?


thanks in advance,
Mathias
 
DF1 on RS232 can reach max 12 meters (sometime I have seen 15 meters for RS232).
You could extend the length with isolated RS232/RS422 converters.

DH485 (which I guess you mean by "AIC network") has a maximum reach of 1219 meters (4000 ft) from end to end. I dont think there is a particular maximum limit between nodes, apart from the total max reach of 1219 meters.
 
Df-1

I've run DF-1 about 65-70 FT. with NO problems on a 5/03. True, good practice is to go 485 but customer needed a 'cheap' fix.
 
RS 232 workaround

I had a customer that was using an older PC on a RS232 Comm port at 60 feet with no problems.The PC failed and we could not find a replacement on site that would work at more than 30 feet without intermittent problems. What a troubleshooting nightmare. We moved the PC to be able to use a 30 feet long Comm cable. We then added cable to the keyboard, mouse, and monitor to reach the original workstation location.
 

Similar Topics

Does anyone know if it is detrimental to use a FULL straight through cable to connect these two. I know that the AB cable does not carry pin 9...
Replies
0
Views
1,975
Tried a straight through 9-pin RS-232 and a null model cable. No luck so far.
Replies
0
Views
1,548
Hi everyone, I am new to this PLC forum and I have a question about this new project I am working on. I have a testing machine running on an old...
Replies
2
Views
1,884
Hi all, I've trawled the search for hours, but couldn't find a definitive answer on this. We have 3 x SLC5/03 processor configured as DF1 Half...
Replies
15
Views
5,001
Hi, Can you communicate to a PLC on the RS-232 port (DF1) after changing the protocol from DF1 Full Duplex to DF1 Radio Modem using RSLinx? I...
Replies
7
Views
7,587
Back
Top Bottom