Automation experts,

Ok, I am converting a ladder program from a mitsubishi controller to another controller and I am trying to figure out one spot on the program. I know there are many users on this board and lots of PLC brands between all of the users. So if anyone can help it would be greatly appreciated. I know that this rung in perticular is a timer but I am not sure of the time base or how it is reset ? (I am assuming it is reset on the same contact M5. The PLC it is from is a Mitsubishi FX0.

....M5............................................... K2
----| |----------------------------------(T0)-----

....T0............................................... M7
----| |----------------------------------( )-----


Thank you,

Dave
 
Last edited:
....M5............................................ ... K2
----| |----------------------------------(T0)-----

....T0............................................ ... M7
----| |----------------------------------( )-----

T0 is an "on delay" timer, the timebase in Mitsubishie FX is 0,01 sec and the timer is reset when M5 goes off.
 
Pego,
First off let me say thank you for the response.
So it will be a total of 2*0.01 = 0.02 second delay correct ?

Thank you,

Dave
 
Dave,
If I am not mistaking about the Mitsubishi PLC, you are right, the delay is 0,02 seconds.

Peter
 
According to my FXo manual (which is 10 years old so may be out of date) T0 to T55 are 100msec timers. If you set M8028 T32 to T55 become 10msec resolution.
 

Similar Topics

How do I convert a float to an integer? I've got a floating-point number D606, value 3999.863. I need to convert it to an integer (4000), then I...
Replies
14
Views
4,146
Hi, Our PLC measures WATER FLOW RATE as an analog input. The PLC reads it as an integer value (D34) in the range 0-4000 as follows: Range...
Replies
12
Views
2,567
Does anyone has any idea to convert a RS422 Signal to RS485 2W ?
Replies
1
Views
2,205
Hello everyone, can anyone help me with covert the STL code to ladder. Iam using plc s71200. A %DB1.DBX33.7 // angel of vaccum...
Replies
2
Views
208
Hello PLCs Forum, I am in a bit of a pickle and was hoping someone could offer me some help. I have a .rss file and just need to see the ladder...
Replies
2
Views
122
Back
Top Bottom