Hey,


Another question about tension on carpet.

I have to change 4 DC-motors by 4 AC-motors (2,2kW). I ordered an S7-315-2DP CPU and 4 MM440 frequency drives. And an OP7. (and much more, but doesn't matter for this topic)

The first motor is Master. the 3 others have to run 10% faster.

Motor 1 2 and 3 have a tension setting on the Operating Panel (OP7). A tension for the carpet. It is needed for other applications that we do on the Carpet, not important for this topic.

The tension must be set from 0-100%

How should I create tension,

Torque control, or speed control with a torque limit ?


thanks
 
Last edited:
I would personally do it completely in speed control. If you put in any torque limit use that only as a machine/product protection. I think you can do better using straight speed-based tension control than you can with a speed/torque hybrid. As I remember this is a surface winder. So ruinning with a base speed reference based on the line speed reference plus a PI tension trim should do the trick.


Keith
 
hi

It's not the surface winder. Because that project was I succes, I had this project with 4 drives and torque control.
 
Your best choice for the follower drives is a combination of speed and torque control. As kamenges states above, a speed regulator with a torque trim would probably be the best arrangement--assuming the drives offer this mode of operation, of course.
 
Combo,

These drives offer speed with torque trim.
Another control (depending on your application) you might
want to look in to is - "droop".
The MM440's have this function too. This works well between two nip
points.
Look at the function diagrams.
 

Similar Topics

We have a mm440 drive that is not starting remotely in automatic. We can control the locally when in hand mode with 0-10v potentiometer. When we...
Replies
5
Views
1,366
Hi all, i m new to this forum. i recently had an assignment where the user wanted to copy parameters from Siemens Micromaster 440 using BOP. Help...
Replies
3
Views
5,762
Hi, I'm using PPO1 to communicate with MM440. I only need to read and modify MM440 parameters, so i sucssesfully use PKW mechanism. I don't have...
Replies
1
Views
1,301
Dear all, Could you please help me a bit? Please check the attached pictures. PIW582 is the signal from the MM440. Act. Filtered torque. In the...
Replies
2
Views
1,482
Sir, I have Siemens mm440 drive .which is using for conveyors .it's speed is controlling through pot (analog input 0-10 volt) But i am facing...
Replies
44
Views
11,295