I have a plc siemens S5 115u cpu 943 B machine was runing smoothly and stopped for break ,but when restarted the following
appears :
1. when switching machine on , the three indicators (QVZ,ZYK,BASP)switched on ,then indicator (RN,ST)switched on .
2. Second step the indicators (RN,QVZ,ZYK)switched off.
3. Third the stop indicator (ST )start flashing and indicator
(BASP)remain on continuously .
N.B.
* All above indicators on cpu .
* The input modules indicators are on .
* The output modules indicators are off (no output).

Thank you in advance
 
abuelfun

With the BASP light on solid this means that the CPU is in 'stop' mode, you also stated that the ST light is flashing.

Would you say that the LED was flashing or flickering?

If the LED is flickering this indicates that the CPU has failed the self test routine, the cure for this is to change the CPU. If the LED is flashing this indicates that there is a memory error.

Paul
 
plc s5 115u , cpu 943B

hello
Paul
Ist of all thank you for your collaboration ,as you said
if the led is flikering the cure is to change cpu ,but in my case the is flashing (memory error), shall i make overall reset
and download new program or what do you suggest.

best regards
 
abuelfun said:
shall i make overall reset
and download new program or what do you suggest.

My knowledge of 'memory faults' is very limited on S5's, but if I had a back up of the original program then I would certainly try a complete wipe of the PLC memory and reload the program.

It is worth a try.:confused:

Paul
 

Similar Topics

Hi, I have tried with the cable IBH S5-USB-Adaptor, communicate with the PLC above, but I can not! The response of the technical assistance of...
Replies
5
Views
3,661
Hi All, I am a Plant Engineer of a Cement grinding and packing factory here in Lae, Papua New Guinea. I have a MEchanical Engineering background...
Replies
3
Views
4,664
Hi, I try to connect Siemens text panel TD17 to S5-115U plc. For PLC to communicate with S5-115U CPU, I need the standard function block and I...
Replies
2
Views
2,136
Hello All, Does anyone know what software and cable is required to get online to a Siemens S5 115U PLC? I need to be able to Upload/Download and...
Replies
6
Views
17,185
HELLO FRIENDS IN ERROR DIAGNOSTICS ON CPU THERE IS A SELECTOR SWITCH RN/ST WITH TWO INDICATORS GREEN/RED . MY QUESTION WHAT IS THE...
Replies
3
Views
4,484
Back
Top Bottom