TOSHIBA MDR40S ouTPUT

jimmyz

Member
Join Date
Apr 2005
Posts
3
Hi all

I was recently asked to program a Toshiba Plc - MDR40S, i have gotten to the point of verifying the input (24vdc), the led lights up to show, i can redirect for the output which works as well, the led corresponds, but when i test for output voltage there is any.

I am in desperate in need of help
 
At a guess; YOU have to supply the voltage.

There is none present but you will see several COMMON terminals. This is where you supply the output voltage. (relay outputs)
 