4 weeks ago I installed a Ultra 3000 indexing servo drive in a bakery and it has worked fine until yesterday when it tripped out with an Error Code 01 'Non-Volatile Memory Endurance Exceeded', which is a unrecoverable error.

I am controlling the drive via DeviceNet from a SLC 5/04 system with a 1747-SDN Scanner. I am using I/O messaging (Output Assembly 9) to start & stop indexes etc and I am not setting the 'Save to NVMEM' bit (Byte 4 / Bit 6).

Any ideas ?
 
My apologies.

The above Ultra 3000 system is operating on a remote site and I have just been given the correct error code of the drive which is E11 not E01.

This make quite a difference. This code is an 'Illegal Hall State' which we have now traced to the encoder plug.

So the moral of the story is always get the fault codes confirmed !

Again, sorry.
 

Similar Topics

Hi, i am getting an error one of our Allen Bradley Ultra 3000i Servo Controllers. The error is E24, which is an excess velocity error. We have...
Replies
1
Views
10,808
After successfully communicating with the Allen Bradley Ultra 3000i 2098-DSD-010X-DN over DeviceNet via a 1769-SDN :) I preceded to configure the...
Replies
4
Views
8,192
My servo motor MPL-B330P-S is controlled by an Ultra 3000i. The problem is that the active position is always different from position command...
Replies
0
Views
1,193
Hi All, I having some problems setting up a new drive using Ultraware. The application is a simple bucket conveyor that indexes along each time...
Replies
2
Views
2,376
Why cant i communicate with drive. I have the cable that is in the manual i have checked my com port. I have the ultra software.
Replies
2
Views
1,910
Back
Top Bottom