Posts
66
Any idea how to increase the rung size (depth) in this dang software beyond the default limit of 8? I am simply trying to OR 10 contacts but the rung limit is 8.

Thanks
 
rocket1010 said:
Any idea how to increase the rung size (depth) in this dang software beyond the default limit of 8? I am simply trying to OR 10 contacts but the rung limit is 8.

Thanks

Take one rung where you OR (i.e) five contacts, take another one where you OR the next five contacts and the result of the previous rung.

:)
 
You can output to an extension as shown:

│(* COMMENT *)

│ SV2+4
├──┤ ├──┬─────────────────────────────────────<+>
│ │
│ SV2+5 │
├──┤ ├──┤
│ │
│ SV3+1 │
├──┤ ├──┤
│ │
│H2SO+RQ│
├──┤ ├──┤




And then add that to the next run as so:

VLV_OVR T_SEC FIL_ALM
<+>─────┬──┤/├─────┤ ├────────────────────────────────(S)──
│ │
│%Q0086 │
├──┤ ├──┤

 
Last edited:
DesertDog said:
You can output to an extension as shown:

│(* COMMENT *)

│ SV2+4
├──┤ ├──┬─────────────────────────────────────<+>
│ │
│ SV2+5 │
├──┤ ├──┤
│ │
│ SV3+1 │
├──┤ ├──┤
│ │
│H2SO+RQ│
├──┤ ├──┤




And then add that to the next run as so:

VLV_OVR T_SEC FIL_ALM
<+>─────┬──┤/├─────┤ ├────────────────────────────────(S)──
│ │
│%Q0086 │
├──┤ ├──┤

If you have a CPU revision 3.? or newer.
 

Similar Topics

Converting a 90-70 LM90 to PME 9.5 and need some help with the migration errors and conflicts in the feed back zone. I have parameterized blocks...
Replies
1
Views
826
Having specific issues with migrating a 90-70 PLC from LM90 to PME 9.5. Backing up the LM90 Folder importing into PME is fine however I do not...
Replies
1
Views
860
We have a customer that has 6 machines running GE Series 90-30 PLCs. In order to support them, they bought a used Dell Full size desktop PC with...
Replies
4
Views
1,243
Hello, one of our clients' GE 90-30 PLCs has lost its program - we deal mostly with AB hardware, so we don't have any old GE programming software...
Replies
2
Views
1,236
Hi Every one, I tried to upload from ge 90-30 plc using versapro software, so that i may migrate program to machine edition. when i try to...
Replies
3
Views
1,574
Back
Top Bottom