Siemens RTD Module Delay...

stevenPLC

Member
Join Date
Sep 2004
Posts
27
Hi,
I encounter a scenario here:

When I connect RTD input into 6ES7 331-7PF00-0AB0 RTD module, it
takes about 5 minutes before able to show actual value. After that, the update will be as per scan time.

I'm using CPU315-2DP.Can anyone tell me why is the delay so long? Any method I can do to prevent this?

Thanks...
 
I've never used this module, so I'm just guessing, but in the manual, under the section "Module filtering modes", there is the statement:

"Additional conversion time for measuring resistance, in ms 185*"

and in the footnotes you find:

"* The resistance measurement for a three-conductor connection is performed every 5 minutes"

I suspect this may have something to do with your problem.

Have you any unused channels? If so are they parameterised as "disabled" (under "meaasuring method") and terminated?

Maybe it's a combination of these things - who knows, with Siemens, it may just be something you have to live with!:confused:
 
6ES7 331-7PF00-0AB0 RTD module Delay Reading..

Hi,

Anyine has any further comment or idea about this issue??


I encounter a scenario here:

When I connect RTD input into 6ES7 331-7PF00-0AB0 RTD module, it
takes about 5 minutes before able to show actual value. After that, the update will be as per scan time.

I'm using CPU315-2DP.Can anyone tell me why is the delay so long? Any method I can do to prevent this?

Thanks...
 

Similar Topics

Hi i use em 231 rtd madule for my project.we have 3 pt-100 that these are serial with each other( 300 ohm),but we have only two end connection of...
Replies
9
Views
5,196
Hi, I have siemens SM1231 RTD module, the temperature I need to read is sub zero. The input is 15 bit plus sign, anyone can suggest the easiest...
Replies
6
Views
2,619
Hi, Anyone knows how is RTD programming in siemens PLC?
Replies
1
Views
1,445
I am trying to use the Siemens S7-300 PLC system to monitor temperature changes using a two wire 100ohm platnium RTD. I am using a SM331 AI...
Replies
2
Views
13,640
Is it possible to use a 3 wire RTD with a Siemens Analog input card without having to linearize the signal prior to the module? The card can be...
Replies
1
Views
7,275
Back
Top Bottom