Hi

I will soon be using one of these cards to control 11 x 115Vac solenoid valves

I will be using MOV's for surge suppression

Should i put 15K 2watt resistors in parallel with the solenoids as AB recommend for limiting the effects of leakage current ?

I normally use OBP 16's or OW8's so am new to this card !

Anything else i should be aware of ?
 
Customer has informed me that the solenoids are 0.6amps 115vac rated

I looked at the OA16 but these are rated at 0.5amps

The OA8 is 1.0 amp rated but i would need 2 of these cards for the 11 valves

I wont be using the OW16's as the customer needs a switching time faster than 10ms the solid state cards offer faster times than the relays.

I wont know for sure until i have seen the valves as sometimes customers can be wrong!

Have you expierence with the OA8 or OA16 ?

Apart from the current loading and blown fuse capability how do these cards differ ?
 
I have experience with the OA16, the only difference I noticed in the spec. sheets was the current capacity. You mentioned that 10 ms was too slow, while it is true that the triac cards turn on in about 1 ms, they take around 10-11 ms to turn off. Might be something to consider. Most of the time I try to use all 24VDC controls if possible, except for motor starters and then I use the isolated input and output cards from Spectrum Controls, (only 8 I/O points per card though).
 

Similar Topics

I had a 1746-HSCE go suspected bad. have to swap the card in the morning. Other than dip switch settings is there any configuration to do?
Replies
1
Views
1,020
Happy Friday everyone! I recently installed a new module, 1746 NIO4I, into the last slot on this chassis. Got the normal IO mismatch fault, added...
Replies
5
Views
1,558
Does anyone know where to get either new or aftermarket 1746-N3 connectors and cables for SLC 32 point discrete in cards? I have a used MCC that...
Replies
1
Views
1,242
I am looking to replace a SLC5/05 processor with an AENTR adapter. Configured the rack in a compactlogix. The connection to all of the cards in...
Replies
5
Views
2,295
Heya guys, I'm looking to connect a Banner Q5XKILAF3000-Q8 (4-20mA) signal into my plc which have a analog input card 1746-NIO4V and was...
Replies
0
Views
1,081
Back
Top Bottom