As for yesterday posting I`m having some problems to interact my rslogic with a slc500....after some precious advices from rsdoran I got out of the previous stall..basically I turn off anything that can use COM 1 and I get to the point where,after I Configure Drive my the communication status is active and the browser finds station 00 "workstation" and 01 SLC-500.
When I go into Driver diagnostic or Station diagnostic everything seems ok,but when I go into rslogic and try to go online the messages are "no response from processor at selected path/node" or "driver AB-PIC-1 not running/configured" and "cannot validate comms configuration"
Any idea what to do....?
thanks marco
 
So far, so good

Now that you've got RSLinx "seeing" the SLC, you're 3/4 of the way there.

First, get RSLinx up and running and seeing the SLC
In RSLogix500, go to the Comms menu and select SYSTEM COMMS.

A smaller version of RSLinx should appear. Open up (click on the '+' of) the AB_PIC-1 driver. You SHOULD see the SLC. If so, click on it, check the box that reads "Apply to Project" in the lower right, and then upload, download or go online as you want to.

If you don't see the SLC, check the status on the line just under the banner of the RSLinx-like popup. If you've selected the AB_PIC-1 driver in the left-hand pane, it should read "BROWSING - node not found". If it says "Not Browsing", you can try unchecking AutoBrowse, and hit the "Refresh" button - sometimes that gives it a kick in the head. Similarly, toggling (Alt+tab) back to the real RSLinx (and confirming that the SLC is still THERE) and then back to Logix might do something.

If all that fails, check which version of RSLogix you are using. There were many fixes to RSLinx to get the PIC to work with NT2K. I think, but am not sure, that there were some fixes to RSLogix too.

Good luck
 

Similar Topics

I`ve been trying to connect my laptop to a couple of slc500 throug a 1747-pic interface converter and after a tried almost every single possible...
Replies
2
Views
3,056
how to delete password protection from rs logic500 (plc is micrologic 1400) i kinow the plc but i want to remove password protection. what is the...
Replies
3
Views
1,617
Hi I am trying to add a AC Servo Linear Actuator, I know that i have to add a axis, but when i am trying to add the motor with catalog number. In...
Replies
10
Views
2,227
I logged on to one of my machines today to try to communicate with the machine (Micrologix 1000) and there are only two plc's on the network, but...
Replies
5
Views
2,122
Hye Does anyone here have the V17 copy. Mind to share? I downloaded but got error during install.
Replies
5
Views
1,856
Back
Top Bottom