huynt Member Join Date Nov 2004 Posts 106 Jun 10, 2005 #1 dear all Do you know different between 1746-Ni8 class1 and 1746Ni8 class3 Thanks
504bloke Lifetime Supporting Member Join Date Jan 2005 Location Down South Posts 2,721 Jun 10, 2005 #2 It explains it quite clearly in the manual here http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1746-um020_-en-p.pdf See pic below for BRIEF explanation
It explains it quite clearly in the manual here http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1746-um020_-en-p.pdf See pic below for BRIEF explanation
Ken Moore Lifetime Supporting Member Join Date May 2004 Location North, West, South Carolina Posts 3,475 Jun 10, 2005 #3 The additional words in the Class 3 are primarily status words, which enable monitoring the module in you ladder logic.