Medium Voltage Cable

mazkhud

Member
Join Date
Jun 2005
Posts
1
I would like to know the minimum acceptable insulation resistance for a 300m cable PVC /XLPE/PVC ,3*150mm^2, SERVICE VOLTAGE IS 6.6KV.
this cble is now isolated from both ends and have 3Mohm resistance measured by 5000v megger.please support your answer by a technical reference.
thank you in advance
 
Last edited:
My rule of thumb was always 1 Megohm per KV + 1 Megohm. That would give a minimum resistance of 7.6 megohm. I see that you are using a cross link PE which in itself can create some problems. In addition, I would never rely on 5,000 volts on a cable carrying more than 6,600 volts. This is a case for DC hipotting a cable using a graduated scale to chart the resistance overtime. Since this is more than megging a cable and not left to novices and definitelysomething I would not explain in an email, I would suggest that you contact the cable manufacturer for help or hire an expert in this field. This is really nothing to take lightly.
 

Similar Topics

Hello everyone, I have read a few threads regarding setting up an AP to wirelessly communicate with PLC networks, but I have a unique question on...
Replies
1
Views
579
Not sure how to word the title but here's my scenario. We have a carriage that moves at high speed with an energy chain and the cable bends in a...
Replies
11
Views
2,870
Hi, Can some explain me what's the measining of this option inside hardware configuration. When should I want/need this option to be...
Replies
3
Views
2,918
Good Morning , I am not too familiar with servo motors. A little bit with robotics. I am looking at an application that has a movement of 0...
Replies
1
Views
1,900
Hiya, I was wondering if you could with a panelview 1000 on (Rsview studio) communicate with a micrologix 1400 on Rslogix 500 ( like on page 1 on...
Replies
5
Views
1,699
Back
Top Bottom