Micrologix communication

ALEX550

Member
Join Date
Jun 2005
Posts
1
My Micrologix 1500 channel 0 blinking, shows communication.
But RsLinx Dose not show the processor.
What should I do to establish communication?
Alex.
 
Did you try Autoconfigure in the COnfigure Drivers area of RS Linx?

If you try this and it doesn't find the PLC, try pushing the COMMS button in the top center of the PLC under the plastic cover and auto configure again.

The comms may be set to half duplex and some other node address. The COMMS button will put the comm. to default while the DCOM LED is lit.
 
Another possiblity is that the comm port is configured for a different protocol than the driver you are using. If you are using DF1 and can't get the driver to autoconfigure while connected to the Micro, kill the DF1 driver, configure a PIC driver and try to communicate using the same cable.
 
cjh said:
Did you try Autoconfigure in the COnfigure Drivers area of RS Linx?

If you try this and it doesn't find the PLC, try pushing the COMMS button in the top center of the PLC under the plastic cover and auto configure again.

The comms may be set to half duplex and some other node address. The COMMS button will put the comm. to default while the DCOM LED is lit.

Good idea. The port could also be set for RS485 instead of DF1. It will auto-config in RSlinx but not show up in RSwho.
 

Similar Topics

Hi all, I had a setup with 2 Micrologix 1100 connected to a Panelview C300 over DH-485. I was mandated to upgrade the HMI, and proposed to...
Replies
5
Views
886
Hello, I'm working on a project in which I need to communicate a Micrologix 1400 series C to a Zebra printer ZD230t through Ethernet/IP. Is there...
Replies
1
Views
747
Having an issue with network timing out when trying to use CIP generic on a Micrologix 1100 B. I’m trying to read flow and totalizer information...
Replies
19
Views
5,012
Hi! Last few I've been trying to send message from MicroLogix 1400 to Micro 850. Unfortunately every time I failed :banghead:. Did someone tried...
Replies
6
Views
3,184
I been tasked with setting up communication between a heating cooling unit manufactured by Advantage Engineering and a Microloagix 1400 plc. The...
Replies
6
Views
2,505
Back
Top Bottom