TConnolly
Lifetime Supporting Member
A single phase transformer has a 480V primary, 50 V secondary. The transformer secondary is connected to a resistive heating load. The transformer primary voltage is controlled by a triac. Under normal operation the primary voltage might be around 315 volts and primary current at around 9 amps, with the secondary current at around 80 amps at about 31 Volts. So far everything is about like I would expect it to be. However, if the primary voltage is raised just slightly with the triac to about 320 - 330 volts then suddenly the primary current jumps significantly to more than 50 amps. There also must be a thermal component associated with it, the jump takes longer to happen if the transformer was off for a period of time.
But now here is the mystery, the secondary output current and voltage does not change when the primary current jumps. Wouldn't the secondary output be expected to change someway if for example a soft-short was developing in the primary winding. A short would have the effect of changing the winding ratio, so shouldn't it affect the output? Is there a way that a transformer can fail that increases the current draw at the primary without affecting the secondary? How unlikely is that?
But now here is the mystery, the secondary output current and voltage does not change when the primary current jumps. Wouldn't the secondary output be expected to change someway if for example a soft-short was developing in the primary winding. A short would have the effect of changing the winding ratio, so shouldn't it affect the output? Is there a way that a transformer can fail that increases the current draw at the primary without affecting the secondary? How unlikely is that?