I have an S5 135U PLC that is loosing inputs to the CPU in as small a time frame as one scan, I.E., the E-stop input should always be on,
I 0.0, unless of course the E-stop circuit is open, I have ran a pigtail from the E-stop controller to another PLC to make sure it is indeed a PLC problem and NEVER loose it on the other PLC, an S5 115U.
I am loosing inputs from different input cards, not just one, as I set up test inputs from spares. The card order in the main rack is CPU, a WF706 encoder card, 4 input cards, 4 output cards (3 regular output cards and 1 relay card, then an expansion card for an ET200 unit that runs the control panel. Is there a way to troubleshoot the problem to the defective component, or is it a swap solution till it goes away, I have already replaced the CPU, power supply, and the PLC rack, and the first input card. Help!!
I 0.0, unless of course the E-stop circuit is open, I have ran a pigtail from the E-stop controller to another PLC to make sure it is indeed a PLC problem and NEVER loose it on the other PLC, an S5 115U.
I am loosing inputs from different input cards, not just one, as I set up test inputs from spares. The card order in the main rack is CPU, a WF706 encoder card, 4 input cards, 4 output cards (3 regular output cards and 1 relay card, then an expansion card for an ET200 unit that runs the control panel. Is there a way to troubleshoot the problem to the defective component, or is it a swap solution till it goes away, I have already replaced the CPU, power supply, and the PLC rack, and the first input card. Help!!