Hi All could anyone give me some advice on how to connect my Micromaster VFD to communicate with a Hedland turbine flow transmitter? I am have some difficulty getting them integrated. Thanks??


T.S
 
I would presume that the Hedland turbine flow transmitter has some output that is an ISA standard. Something like a 0-10VDC, 4-20mADC or 1-5VDC or a digital pulse train or something that is available and defined in the specs for the transmitter. Once you know what you have coming from the flow transmitter, look at the available analog inputs to your drive and see is they are compatible. If they are you are home free, if not, then you may have to do some signal conditioning to get the two to communicate. For instance, if the flow transmitter only outputs a 4-20mADC signal, and the drive only accepts a 0-10VDC signal, then a conditioner that will change the current signal to a voltage signal is what you will have to use. Simple enough, huh?

 
The transmitter puts out a 4-20ma signal and the VFD accepts 4-20ma signal.

I have got a rheostat wired in to the analog input to adjust the speed of the VFD and now I want to add a flow transmitter to monitor the flow. The problem is the drive only has one analog input. Can I do this?

T.S
 
The answer lies entirely with the features contained within the VFD. If the drive has PID capability, wire it according to the instruction manual. If the drive does not have PID capability, you will need a stand-alone PID controller ahead of the drive. In that case, your setpoint pot and your flowmeter both connect to the controller, not the drive.
 

Similar Topics

Hello, first of all let me state for the record that I'm not a tech of any kind, I have limited experience with industrial automation devices, so...
Replies
0
Views
11
Sorry in advance for the long post, but this requires a little back story. I work in a facility with a couple hundred VFDs Most are in a web...
Replies
13
Views
97
Customer want to use contactor for their 5HP motor blower application. im leaning to VFD. anyone use contractor for blower application...
Replies
9
Views
179
Hi, I would like to assemble a simulator/practice booster pump system that uses PID to maintain steady water pressure under various outlet demands...
Replies
0
Views
74
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
136
Back
Top Bottom