Greetings fellows,Iam new to here but here is my problem : purchased a AB micrologix plc stater kit with windows based software RSLOGIX 500 and RSLINX, however cannot get plc to talk to pc, yet drivers are configured and micrologix is displayed on pc any ideas to source this solution?
Chris,
United Kingdom.
 
Last edited:
Interesting...

and micrologix is displayed on pc

by this do you mean that the MicroLogix icon is appearing in the RSLinx Who display?

Is the Autobrowse box ticked and can you see Linx scanning for nodes?

Can you right click on the Micro and get Station Diagnostics or do Data Monitor... if you can do any of these things then the PLC is connected to the PC.

If not then the next issue is to resolve why RSLogix is not connecting to the RSLinx driver.
 
Along the same lines as Phillips questioning, Can you see the little Icon of the Micrologix Controller?
RSWho.jpg
 
If you were closer id pop by and help, but i have not been up your way for a few months now!

I have used an ML beofre only the SLc's but i would assume they are very similar

So if you can see the ML in RS Linx as Micro then the coms from linx to the micro should be ok

Go into RS Logix and click

Comms > System Comms

should bring up a window as below

(I have no online plcs at home so the ONLINE button is greyed out but yours should be highlighted)

Click the Online button and see what happens
 
Please forgive me if I am stating the obvious.
Once you get RSlinx to recognize the PLC you need to start RSlogix to Go Online.
Start up RSLogix
Then Click Go Online.
Go.jpg

You can select one of the buttons to the right,
Online.jpg

Is this of much use?
George Bradley
 
What two posters have mentioned is that once you get the RSLinx driver configured, you also have to configure RSLogix 500 software to use the specific "path" to the controller.

The path includes the driver name, and the network node of the controller. Because you're just using DF1 Full Duplex, the controller's node number will be 1.

RSLogix 500 includes a "Who Active Go Online" function that allows you to select the driver and node number, and it also saves the last driver and node number you were using.

Again: The RSLogix 500 software must be made aware of the proper RSLinx driver and controller node number. Use the "System Comms" or "Who Active Go Online" functions.

Did your starter pack come with the "getting results" document for RSLogix 500 ? This is really Day 1 stuff in the SLC/Micrologix classes I teach.
 

Similar Topics

Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
Replies
8
Views
605
Hi there I am new with this thing and i don't know how to connect Allen Bradley Micrologix 1200 PLC to Raspberry Pi using USB to RS485 in NodeRED...
Replies
3
Views
2,266
Hello everyone, So on Monday morning I'm expecting to have a box of random parts dumped in front of me. I'll create another thread with more...
Replies
1
Views
1,965
Hey Everyone, We have a Micrologix 1400 (1766-L32BXB) with a Panelview 800 7" Screen, the Micrologix also has a 1762-IQ16 Input Card and a...
Replies
2
Views
1,286
Hello guys, I just noticed that RS don't stock Micrologix output modules anymore. Is it true to assume that the Micrologix series is becoming...
Replies
14
Views
3,427
Back
Top Bottom