PanelView_Blues

Join Date
Jul 2005
Location
Manchester
Posts
1
I have a 2711-T10C20 Panelview 1000, tried to connect via Ethernet...no go. The Panelview is connected to ABs 9300-RADES Modem, the other connection goes into Mencom Ethernet connection and Logix 5000 rack. If I connect thru the Mencom, I can see and talk to the Logix 5000, I cannot however talk to the Panelview. I am using Panelbuilder32. The Panelview and Logix 5000 talk without issue. I was under the impression that I could use the RS-232 port on the Panelview, and that the printer portion was switchable. I tried thru RS-232 as well with a straight and null connection, no go as well. Any help would be greatly appreciated. RSLinx Lite 2.42 Build 18
 
I found it is easier to connect with a ethernet switch instead of 9300-rades. You could use any connect the panelview,logix 5000, and the 9300-rades to the switch and it should work fairly easy.

Pat
 

Similar Topics

Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
42
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
157
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
69
saludos a toda la comunidad Hace unos días he venido presentando pérdida de comunicación en una terminal hmi, anexo las imagenes de la secencia...
Replies
1
Views
100
Hello everyone. This is more of an HMI issue. I have a new PanelView Plus 7 Series B. I am using the alarm list object to display the fault...
Replies
0
Views
87
Back
Top Bottom