CLX DH+ Panelview help

allscott

Member
Join Date
Jul 2004
Posts
1,332
I'm trying to set up a CLX processor to a PV 600 via DH+. We are new to control logix and are having trouble figuring out how to address the tags in the panelview.

Using the CLX tags under the tag address in the panelview doesn't seem to work and CLX doesn't have "real" memory addresses ie:N7:0.'

What am I missing?
 
Basically, since the Panelview won't use CLX tags, you have to use PLC5 style addresses.

In RSLogix5000, on the main menu, select "Logic", then "Map PLC/SLC Messages...". The dialog will allow you to map a PLC5 style file number to a CLX tag. The CLX tag should be an integer array.

Good luck,

Mike Ellis
 