What is the longest distance you can run an RS232 cable from a PLC to a field device?

I have an application where the distance is about 100ft. I have read that it is a good idea to keep the length under 50ft.

 
RS232 spec will say 50 ft. I have gone as much as 175 feet without problems. Shielded wiring ,dicated conduit.
 
Extending RS-232 beyond 50 feet

The RS-232 spec simply suggests that a maximum distance of 50 feet is more or less "guaranteed", though I've had numerous customers exceed this. Factors that can diminish your performance across longer distances can include, but are not limited to heavy RF "noisy" environments, and even fluorescent lighting. If you're looking to extend beyond 50 feet, ******* makes a DeviceMaster RTS product which offers RS-232 to Ethernet connectivity, so that your RS-232 serial cable run can be within the 50 feet limitation, and then standard CAT 5 Ethernet cable for the longer runs... For simplicity sake, you could even put a second DeviceMaster RTS on the other end of this run and simply "tunnel" between these two units. Please feel free to contact me for further details.

Jason Reiling
*******
763-494-4144
 
As others have said:

Capacitance: Lower is better. Look for EDDC = Extended Distance Data Cable.

Voltage of the devices: Using devices that have a +15v to -15v signal switch requires more drive than -3v to +5v.

Baud Rate: Most of the times lower baud = longer length = better signal.


Consider using a current loop for high noise, long length runs. Black Box (Blackbox.com) has my prefered brands that I've used up to about a mile and take RS-232 at each end. Some can be powered by the CTS/DSR signals present on the serial devices.

Also consider RS-422 converters at each end, but most people try to use them with 2 wires and should have used 4 wires. Better brand Current loop converters can do full duplex over 2 wires.
 
If you can afford them, get yourself some RS-232 to Fiber Optics converteres...and some fiber. There are a lot of good ones in the market, like B&B Electronics, they can convert almost anything.

Somehow, the benefit is high and the relative price is low.
 
Thanks for all the help!
I am going to use the Belden blue hose for the RS232 cable since I am only using pins 2,3,and 5. I think that this will be a good shielded cable for the application.
 

Similar Topics

i have an device which can support serial (RS485,RS232),CAN protocol . i want to connect it to an existing MIB 1553B bus ,what device will I need...
Replies
0
Views
87
Hello: I have to connect a RS232 Modbus RTU slave that only has Tx, Rx and GND signals to a Modbus RTU master. However, all RS232 to RS485...
Replies
3
Views
225
Hi to everybody. I need to read the first 12 characters of the message that a barcode reader sends to the ascii card (1734-rs232 ascii) and I...
Replies
8
Views
718
I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
Replies
14
Views
2,543
I'm trying to manually convert a Beijer E200 HMI project onto to a new Mitsubishi GOT gs2107-wtbd. The PLC is a very old A-series AS1CPU and is...
Replies
1
Views
374
Back
Top Bottom