We are using Prosoft MV146-MCM module for SLC family
I had completely gone through the manual. Its really an amazing card. My requirement is that I had to use this cad as a slave & to make available all SLC data. I had made the following changes in the SAMPLE program already provided with the card
Suppose N10 is MCM CFG (Configuration file) data file
Then I do
N10:10 1 Port 1 Enabled
N10:11 1 Slave
N10:16 9600 Baud rate
N10:24 2 Slave ID
N10:25 0 P1_Bit Offset
N10:26 0 P1_Word Offset
N10:27 0 P1_OutputOffset
N10:28 0 Holding _ Offset
In sample ladder program I only made following changes
My SLC configuration is as under
Slot 1 MV146-MCM
Slot 2 1746-IV16 (Digital Input card)
Slot 3 1746-OW16 (Digital Output card)
I also want to make available B3:0/0 to B3:1/15(Two words)
Plus T4:0.PRE to T4:3RE (Presets values for four timers)
I simply use copy commands as under
Source Des LENGTH
COP #I:2.0 #N32:0 1
(Where N32 is write data & 200 words of this has already been copied to MI:1.0 to M1:1.199 in sample program)
COP #O:3.0 #N32:1 1
COP #B3:0 #N32:2 2
MOV T4:0.PRE N32:4
MOV T4:1.PRE N32:5
MOV T4:2.PRE N32:6
MOV T4:3.PRE N32:7
I cannot check it as I don’t have actual card I had only the sample ladder program provided by Prosoft & I had made above mentioned changes
I had mapped these M1 files with mode bus registers as under
Modbus Function Prosoft M1 Nfile PLC Address
Address Code Address
For Digital Inputs
Modbus Address---Function Code--Prosoft M1Address---N file---PLC Address
10001 02 M1:1.0 N32:0.0 I: 2/0
10002 02 M1:1.0 N32:0.1 I: 2/1
…………………………………………………………………….
10016 02 M1:1.0 N32:0.15 I: 2/15
For Digital Outputs
10017 02 M1:1.1 N32:1.0 O: 3/0
10018 02 M1:1.1 N32:1.1 O: 3/1
…………………………………………………………………….
10032 02 M1:1.1 N32:1.15 O: 3/15
For internal bits (32 bits)
00033 01 M1:2.0 N32:2.0 B3/0
00033 01 M1:2.0 N32:2.1 B3/1
…………………………………………………………………….
00048 01 M1:2.0 N32:2.15 I: 2/15
00049 01 M1:3.0 N32:3.0 B3/16
00050 02 M1:3.0 N32:3.1 B3/17
…………………………………………………………………….
00064 01 M1:3.0 N32:3.15 B3/31
For Timer Presets (4 timer preset values)
40005 04 M1:4.0 N32:4 T4:0.PRE
40006 04 M1:5.0 N32:5 T4:1.PRE
40007 04 M1:6.0 N32:6 T4:2.PRE
40008 04 M1:7.0 N32:7 T4:3.PRE
I just want to know that my mapping is correct or need any modifications
I am on a plant & I need your prompt favor
Anxiously waiting for your reply
I had completely gone through the manual. Its really an amazing card. My requirement is that I had to use this cad as a slave & to make available all SLC data. I had made the following changes in the SAMPLE program already provided with the card
Suppose N10 is MCM CFG (Configuration file) data file
Then I do
N10:10 1 Port 1 Enabled
N10:11 1 Slave
N10:16 9600 Baud rate
N10:24 2 Slave ID
N10:25 0 P1_Bit Offset
N10:26 0 P1_Word Offset
N10:27 0 P1_OutputOffset
N10:28 0 Holding _ Offset
In sample ladder program I only made following changes
My SLC configuration is as under
Slot 1 MV146-MCM
Slot 2 1746-IV16 (Digital Input card)
Slot 3 1746-OW16 (Digital Output card)
I also want to make available B3:0/0 to B3:1/15(Two words)
Plus T4:0.PRE to T4:3RE (Presets values for four timers)
I simply use copy commands as under
Source Des LENGTH
COP #I:2.0 #N32:0 1
(Where N32 is write data & 200 words of this has already been copied to MI:1.0 to M1:1.199 in sample program)
COP #O:3.0 #N32:1 1
COP #B3:0 #N32:2 2
MOV T4:0.PRE N32:4
MOV T4:1.PRE N32:5
MOV T4:2.PRE N32:6
MOV T4:3.PRE N32:7
I cannot check it as I don’t have actual card I had only the sample ladder program provided by Prosoft & I had made above mentioned changes
I had mapped these M1 files with mode bus registers as under
Modbus Function Prosoft M1 Nfile PLC Address
Address Code Address
For Digital Inputs
Modbus Address---Function Code--Prosoft M1Address---N file---PLC Address
10001 02 M1:1.0 N32:0.0 I: 2/0
10002 02 M1:1.0 N32:0.1 I: 2/1
…………………………………………………………………….
10016 02 M1:1.0 N32:0.15 I: 2/15
For Digital Outputs
10017 02 M1:1.1 N32:1.0 O: 3/0
10018 02 M1:1.1 N32:1.1 O: 3/1
…………………………………………………………………….
10032 02 M1:1.1 N32:1.15 O: 3/15
For internal bits (32 bits)
00033 01 M1:2.0 N32:2.0 B3/0
00033 01 M1:2.0 N32:2.1 B3/1
…………………………………………………………………….
00048 01 M1:2.0 N32:2.15 I: 2/15
00049 01 M1:3.0 N32:3.0 B3/16
00050 02 M1:3.0 N32:3.1 B3/17
…………………………………………………………………….
00064 01 M1:3.0 N32:3.15 B3/31
For Timer Presets (4 timer preset values)
40005 04 M1:4.0 N32:4 T4:0.PRE
40006 04 M1:5.0 N32:5 T4:1.PRE
40007 04 M1:6.0 N32:6 T4:2.PRE
40008 04 M1:7.0 N32:7 T4:3.PRE
I just want to know that my mapping is correct or need any modifications
I am on a plant & I need your prompt favor