micrologix1200 error

indra

Member
Join Date
Apr 2005
Location
indonesia
Posts
161
I have problem with MICROLOGIX1200, the fault LED flashing ( RUN LED off ).
I want to check the error message, but the communication ONLINE error "NO RESPONSE FROM PROCESSOR SELECTED PATH/NODE. DIAGNOSTIC STATUS FAILED : 0x4"
even I choosed the right type the communication line DF1-1 and check on the RSLINK, this node is found and status RUNNING.
I also can not download the program because I can not go ONLINE.
Does anybody knows how to solve this problem ? What is the meaning of 0x4 ??

indra
 
that error simply means that RSLogix500 cannot connect to PLC using last configured connection.
if you can see plc in rSLinx, driver setting is correct otherwise try Autoconfigure button.
once the RSLinx is ok, go to RSLogix, from menu Comms, select
System Comms and use RSWho to navigate to node you wish to connect to. Notice "Apply to Project" checkbox. If you place mark in it, it will remember this connection for future use. error you see now is result of this, your RSLogix is using incorrect settings or maybe wrong driver (or the RSLinx is not connected to PLC).
 
i'm not sure if this would work for micrologixs but i had the same error come up with a SLC 5/04 i was using rslogix500 as well. All i did was reset the factory settings on the card set it back up in rslogix500 then downloaded the program in and it worked fine from there. Like i said i'm not sure if it's the same for micrologix but you could look into it.
 

Similar Topics

I have a micrologix 1200 and I am trying to get a barcode scanner to talk to the COM 0 port. I know the scanner baude rate is 9600 because I...
Replies
0
Views
1,769
I have a micrologix 1200 that will run one of three different timing sequence, depending on which input is triggered. I'm trying to find the best...
Replies
6
Views
3,454
How to check the communication between the Micrologix1200 to Citect SCADA. I use PLX51-DF1-ENI router to communicate in scada. I tried to use...
Replies
0
Views
1,342
Good day all. I have a some MAC bullet valve catrtidges (BV210A-CA1-00-BEH0-CTC). They control vacuum for suction cups that pick up various...
Replies
0
Views
1,610
Can I communicate to a Micrologix 1200, going through a Panelview C600? I have this machine made by SIDEL that has a Micrologix 1200 talking to a...
Replies
4
Views
1,479
Back
Top Bottom