Looking for some information concerning Class I div I or div II panels. We are building a control panel that is mostly going to be a junction box for instrumentation and several motors. No starters or relays will exist in this panel, but there are several I to P converters. The customer has no classification for the room where this is going, there is the possibility in the event of leakage a small amount of hydrogen may escape into the atmosphere.( I cannont define "small amount") The control panel will be mounted on to a system skid. My question is, does this become a class I div II area where there is not normally going to be hydrogen in the area under normal operation? Or is it a class I div I area since in the event of a rupture there is the potential for hydrogen in the area? I am somewhat new to this and the NEC is a bit confusing when it comes to the div I or div II. We are planning on using a purge on the panel and I just want to make sure we use the right one. Also we are taking in RTD’s signals, some 4-20 signals, do IS barriers need to be supplied if the cables are going into a purged panel? Hope my questions make sense and thanks for the help.
 
Being a control panel guy, I suggest that you check out Hoffman's (the enclosure people) website at:

http://www.hoffmanonline.com/Technical_Info/

Especially look under the tab of "Hazardous Locations". You can do a variety of things to meet the safety requirements, but you really need to know exactly what you are facing in the way of the presence of explosive gases. You can't take safety lightly!

Hoffman, for one, has a few "purge" packages they offer. I'm sure other vendors do also. Check out their technical resources so you get the one that's right for your application

DISCLAIMER: I only mention Hoffman because I use them a lot. I don't work for them.
 
Division 2

This would be classified as a division 2 because the egnitable substance will only be present under abnormal conditions.

As far as the prevention factor go, purging the box only keeps that area in the box safe, what about other connections in the zone area.

Safety barriers are mostly used, they limit the capacitance and inductance in the loop and clamps when it exceeds the barriers allowed values in Div 1 loops and you must make absolutely sure about the classification.

The instruments that you use must be classified to your zone div 2.

Here is a helpfull link

http://www.hubbell-canada.com/whitePapers/wiring/codesSWP.asp

On this site is a table showing you what certification for which zones and divisions.

Hope it helps

Rheinhardt
 
Last edited:
Stooperbike, the first thing to be done is have them determine the classification of the area. I cannot do it, you cannot do it, RheinhardtP can only guess at it. The customers insurance Co, safety person, the local fire marshall and others will do it.

Get that done and then you can procede. Until they, only guesses will be had. You may be surprized that the area gets no classification, thus no need for any purge & I./S. barriers.
 
Another link

Here is another helpfull link

http://www.iaei.org/foc/cmp14.htm

theDAve2 is 100% right we can only assume using the code as a guideline and what you tell us, you should get the cetification authority for explosion prevention.

From the link

In Class I, Division 1 locations, it is assumed that ignitible concentrations will exist under normal operating conditions. An acceptable level of safety for the electrical system has been determined to include at least two failures before the system can ignite the atmosphere. In Division 2, there has to be some abnormal condition (failure of containment of the flammable material, failure of ventilation, etc.) before an ignitible atmosphere can exist. Therefore ignition could only occur in Division 2 when the containment of the material and the nonincendive circuit failed simultaneously (two faults).

Hope this helps with your confusion regarding Div 1 and Div 2.

Regards

Rheinhardt
 
Yes the definitely helps, I am going to go back to the GC and find out what I am supposed to supply. I am concerned about liability, I do not want to be panel guy that causes a fire or explosion. The customer asked for a purge, in there eyes a needle valve with bulkhead fitting into cabinet was fine, no vent, no regulator, I am planning to supply this with a type Z air purge kit. To add another layer I am a contractor for the GC so my involvement with the customer is limited, my GC called out Class I div II but I am not sure were he got that info from. On top of that we are copying an existing system that has no air purge in the panel, but the panel is in a different room. Maybe I’ll tell them the panel shop is closed and to go away, :)



Thanks for the feed back, I could not sleep last night thinking about this!!!!
 
In my humble opinion, based on 20 years of working around hazardous areas, your panel will be in a Class 1, Division II area (not normally hazardous, but can be if something fails or leaks). By all means get a definition of the area if possible. My experiences with this question is that usually you get a long run-around from all parties, no one wanting to make the decision, hoping to pass the buck, or delay making a decision until the need goes away. No company or person wants to put his nead in the noose, in case something goes boom!

An air purge is a good solution. You probably know that your conduits leaving the Division II cabinet and ending in the Division I area, are supposed to be sealed with approved conduit seals poured with sealing compound.

The best way to handle electrical sparking devices in a Class 1 area is to re-locate as many devices as possible into a non-hazardous area.
 
Last edited:
You will need the exact classification, not just Class I, Div II, but something like Class I, Div II, Groups B & D. I believe Hydrogen is group C.

Any and all devices used must be rated not only for Class I, Div II, but also for group C.


Ken
 
Stooperbike,
You really need written documentation from the GC AND Architect specifying the EXACT Class, Division, and Group. Don’t build or design anything with out that information delivered to you on a signed letterhead from the specifier. Actually this information should be plasterd all over the job specs, contract and other documentation.

 
I would agree that you don't want to become the AWJ, or "authority with jurisdiction". That's a big hat to wear. Also, I would consider installing H2 detectors- hydrogen is nasty stuff with a low LEL.

Good luck!

K
 

Similar Topics

I'm looking for some clarification if anyone here is familiar with UL698a panels. Panel is out of zone/class'd area. with thermocouples extending...
Replies
0
Views
112
Hi - I am searching for an M12 panel receptacles to use for ethernet connections. I see lots of M12 cables that are ATEX / C1D2 rated but nothing...
Replies
2
Views
958
Can someone please recommend a signal light tower that can be used in a Class 1 Div 2 Classified area? Explosive gasses can be present under...
Replies
4
Views
1,711
Hi everyone, I have a customer looking for a printer that has Class 1 Division 2 rating. I would like it to have a Ethernet connection and be...
Replies
0
Views
1,169
Are there any code experts out there that can point me to a reference to support not using a Solenoid DIN connector with a LED in a Class 2 Div 2...