This week I was called in to "fix" some control issues with a set of 3 pumps in a remote northern village.
The setup was one master control PLC with a serial modbus radio transmitter and 3 remote pumps (10 miles away).
The remote controlers had only water levels and flowmeters analog inputs and digital I/O, the pressure sensor was at the main site.
So they had a lot of spikes and lows. I figure the PID was not stable. Once I looked at the control loop, they had a PID but no analog loop to control any pumps. They had a set of points where some pumps would start alone or in combination witht another up to all pumps ON.
No water tower!
Wow, quite a chalenge. I manage to get the system not to cycle to fast and be within ±10 PSIG of the setpoint. (SP=65 PSIG)
To do this I had to add some pretty precise conditions that delt with there fire-pump and holding tank filling but it worked. I will of course submit some recommendation about using VFDs but here is something that fascinate me during the days I observed the water supply.
Pump # 1 alone would give us 180 GPM at 65 PSIG, if I open a BIG leak it could go up to 240 GPM at only 35 PSIG
Pump # 2 alone would give us 270 GPM at 65 PSIG, if I open a BIG leak it could go up to 390 GPM at only 35 PSIG
Pump # 3 alone would give us 170 GPM at 65 PSIG, if I open a BIG leak it could go up to 275 GPM at only 35 PSIG
Now, ALL Pumps ON would give us 480 GPM at 65 PSIG, if I open a BIG leak it could go up to 510 GPM at only 35 PSIG
If we added the "alone" readings we got 620 GPM at 65 PSIG and 905 GPM at only 35 PSIG
I understand that the pressure variation augment to the square of the speed variation but the difference between 2 pumps runnig at max Flow was only 10% from 3 pumps. We got about 450 GPM with 2 pumps and 480 with 3 of them.
A soon as we would start the third pump we could see the flow drop sharply on the 2 other pumps.
Can you expand on this?
Thanks in advance.
The setup was one master control PLC with a serial modbus radio transmitter and 3 remote pumps (10 miles away).
The remote controlers had only water levels and flowmeters analog inputs and digital I/O, the pressure sensor was at the main site.
So they had a lot of spikes and lows. I figure the PID was not stable. Once I looked at the control loop, they had a PID but no analog loop to control any pumps. They had a set of points where some pumps would start alone or in combination witht another up to all pumps ON.
No water tower!
Wow, quite a chalenge. I manage to get the system not to cycle to fast and be within ±10 PSIG of the setpoint. (SP=65 PSIG)
To do this I had to add some pretty precise conditions that delt with there fire-pump and holding tank filling but it worked. I will of course submit some recommendation about using VFDs but here is something that fascinate me during the days I observed the water supply.
Pump # 1 alone would give us 180 GPM at 65 PSIG, if I open a BIG leak it could go up to 240 GPM at only 35 PSIG
Pump # 2 alone would give us 270 GPM at 65 PSIG, if I open a BIG leak it could go up to 390 GPM at only 35 PSIG
Pump # 3 alone would give us 170 GPM at 65 PSIG, if I open a BIG leak it could go up to 275 GPM at only 35 PSIG
Now, ALL Pumps ON would give us 480 GPM at 65 PSIG, if I open a BIG leak it could go up to 510 GPM at only 35 PSIG
If we added the "alone" readings we got 620 GPM at 65 PSIG and 905 GPM at only 35 PSIG
I understand that the pressure variation augment to the square of the speed variation but the difference between 2 pumps runnig at max Flow was only 10% from 3 pumps. We got about 450 GPM with 2 pumps and 480 with 3 of them.
A soon as we would start the third pump we could see the flow drop sharply on the 2 other pumps.
Can you expand on this?
Thanks in advance.