Where can I get info on Fanuc Ladder data types?
example: F0126.3
I can program Allen-Bradley and Automationdirect PLC's even some SquareD stuff but I'm lost with the fanuc's.
I know what x and y are(inputs and outputs) but I need to find out where I can look up values or states for R values and F values. Where can I get information on how to get started.
Thanks for any help...
 
EDIT: I am feeling bad today so may not have read the question thoroughly. My answer relevant 90-30, 90-70 and VersaMax ladder logic...I am not sure what the F is refering too. I havent worked with GE for awhile so hopefully Steve or Russ will clarify the issue and any mistakes I have made.

Discrete
%I The %I prefix represents input references. %I references are located in the input status table, which stores the state of all inputs received from input modules during the last input scan. %I memory is always retentive.

%Q The %Q prefix represents physical output references. %Q references are located in the output status table, which stores the state of the output references as last set by the application program. This output status table's values are sent to output modules at the end of the program scan. A particular %Q reference may be either retentive or non­retentive, depending on its use in the program.

%M The %M prefix represents internal references. A particular %M reference may be either retentive or non­retentive.

%T The %T prefix represents temporary references that are used many times in a program. Data with %T references is not retained through power loss or Run-to-Stop-to-Run transitions. %T references cannot be used with retentive coils.
%S The %S, %SA, %SB, and %SC prefixes represent system status references. These references are used to access special PLC data such as timers, scan information, and fault information. For example, the %SC0012 bit can be used to check the status of the PLC fault table. Once the bit is set on by an error, it will not be reset until after the sweep.

%S, %SA, %SB, and %SC can be used on any type of logic contact.
%SA, %SB, and %SC can be used on retentive coils ­(M)­
%S can be used as inputs to functions or function blocks.
%SA, %SB, and %SC can be used as inputs or outputs to functions and function blocks. %S, %SA, %SB, and %SC references are non­retentive.

%G The %G, %GA, %GB, %GC, %GD, and %GE prefixes represent global data references. These references are used to access data shared among several PLCs. %G, %GA, %GB, %GC, %GD, and %GE references can be used on contacts and retentive coils, but not on non­retentive coils

Register

%R Use the prefix %R to assign system register references, which will store program data such as the results of calculations.

%AI The prefix %AI represents an analog input register. This prefix is followed by the register address of the reference (for example, %AI0015). An analog input register holds the value of one analog input or another value.

%AQ The prefix %AQ represents an analog output register. This prefix is followed by the register address of the reference (for example, %AQ0056). An analog output register holds the value of one analog output or other non-discrete value.

%P (Series 90-70 only) Use the prefix %P to assign program register references that will store program data from the _MAIN block. This data can be accessed from all program blocks. The size of the %P data block is based on the highest %P reference in all blocks. This reference type is scoped at a program level and is therefore only visible to LD programs.

%L (Series 90-70 only) Use the prefix %L to assign local register references that will store program data unique to a block. The size of the %L data block is based on the highest %L reference in the associated block. This reference type is scoped at a program level and is therefore only visible to LD programs.

Note: All register references are retained across a power cycle to the CPU. In 90-70 PLCs, you can use indirect referencing for all register references (%R, %AI, %AQ, %P, and %L) to identify a location in memory that contains the offset in the same memory type of the data to be used.
 
Last edited:
Fanuc Ladder III is the software for programming the ladder task in CNC controllers, not for GE Fanuc PLCs. As such, it's not the best place to learn about GE Fanuc PLC products. Furthermore, the manuals for Fanuc CNC controllers are about the worst examples of Jenglish translation I've ever run across.

Fanuc Ladder III is included in the suite of products under the Cimplicity Machine Edition software. The help files for that product would be a good place to start.
 
I found it in the ole Maintance manual:
Fxxx.x is a bit address comeing from thr NC to the PMC
Rxxx.x is an internal coil
P is a Sub program
Kxxx.x is a Keep relay
 

Similar Topics

Old Allen Bradley guy here: I used to have a SCL or SCP and then a PID tuner block to use. Here in the FANUC ladder world I have not been able to...
Replies
3
Views
1,870
Hi... I cant able to view 0i-F series logic in Fladder III 5.80 version. Should i need to update or anything else?
Replies
0
Views
1,094
Hey can anyone help me. I'm working with Fanuc Ladder III and I have 2 questions. 1) Under relay comment you are only allowed 16 characters I...
Replies
1
Views
3,399
Hello Everyone, I would like to get some advice from seniors!! Currently, I involve in writing PLC logic and Robot programs (ABB rapid...
Replies
5
Views
3,884
Can anybody here explain how do we know the number on address at fanuc ladder diagram? ex : Y0003.0 , F0000.6 , X0008.4 , R0552.0 , etc i don't...
Replies
2
Views
3,532
Back
Top Bottom